You can tie-in multiple low point drains on dry systems together. it's actually a "shall" for multiple branchlines. NFPA 13 2013 & 2016 8.16.2.5.3.6 Tie-in drains shall be provided for multiple adjacent trapped branch pipes and shall be only 1 in. (25 mm).Tie-in drain lines shall be pitched a minimum of 1⁄2 in. per 10 ft(4 mm/m). This section was moved to 16.10.5.3.6 in 2019.
I don't see any reason you couldn't provide tie-in drains post drum drip either. Jamie Seidl On Wed, Jan 31, 2024 at 4:53 PM Taylor Schumacher <[email protected]> wrote: > I remember seeing something that says you cannot combine dry system drains > together, but I cannot find it. FWIW, this would be post drum drips. > > > > Thanks, > > > > > > *Taylor Schumacher* > > > > _________________________________________________________ > SprinklerForum mailing list: > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org > To unsubscribe send an email to > [email protected] >