If these are electric pumps, power to the pumps must be sufficient such that
both can operate as anticipated.
Also, NFPA 20 has required the following for fire pump field acceptance flow
testing since 2010:
Where simultaneous operation of multiple pumps is possible or
required as part of a system design, the acceptance test shall
include a flow test of all pumps operating simultaneously.
Hope this helps,
Ryan L. Hinson, PE*, SET** \ Burns & McDonnell
Associate Fire Protection Engineer \ Upper Midwest Region
O 612-900-3755 \ M 763-688-4045 \ F 952-229-2923
[email protected]<mailto:[email protected]> \
burnsmcd.com<http://www.burnsmcd.com/>
8201 Norman Center Drive, Suite 500 \ Bloomington, MN 55437
*Registered in: AK, LA, MD, MN, PA, TX, & UT
**NICET IV - Water-Based Systems Layout
From: Eric Rieve <[email protected]>
Sent: Monday, January 29, 2024 11:17 AM
To: Discussion list on issues relating to automatic fire sprinklers
<[email protected]>
Subject: [Sprinklerforum] Re: Fire Pump testing procedures
NFPA 25 added a section regarding this in 2023.
8.3.3.11: Where simultaneous operation of multiple pumps is required to meet
the water-based system demand for flow and pressure, the requirements of
8.3.3.10(2) shall be repeated at each flow condition with all pumps operating
simultaneously.
So, your test-header will need to accommodate the combined flow.
Hope this helps!
Eric Rieve, SET
Rieve Fire Protection
From: Fpdcdesign <[email protected]<mailto:[email protected]>>
Sent: Monday, January 29, 2024 11:51 AM
To: Discussion list on issues relating to automatic fire sprinklers
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: Fire Pump testing procedures
I would think you would need to do both, at least initially. Individually to
find out that each pump is working correctly itself and both to verify that the
full demand can be met.
For a future testing program, probably something specialized would be needed.
Make sure it is available in writing.
On Jan 29, 2024 at 11:45 AM, <Craig Prahl<mailto:[email protected]>> wrote:
I have a project that requires two 1500 gpm pumps to meet the most demanding
system requirements. Client doesn't want any pumps over 1500 gpm. Long story.
As far as testing, would you test each pump individually or together or ??
Trying to establish what we need as far as a test header.
Thanks.
Craig Prahl | Jacobs | Fire Protection SME - Special Hazards |
[email protected]<mailto:[email protected]> |
www.jacobs.com<https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$>
1041 East Butler Road Greenville, South Carolina 29606
CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS
________________________________
NOTICE - This communication may contain confidential and privileged information
that is for the sole use of the intended recipient. Any viewing, copying or
distribution of, or reliance on this message by unintended recipients is
strictly prohibited. If you have received this message in error, please notify
us immediately by replying to the message and deleting it from your computer.
_________________________________________________________ SprinklerForum
mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To
unsubscribe send an email to
[email protected]<mailto:[email protected]>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]