I would think you would need to do both, at least initially. Individually to 
find out that each pump is working correctly itself and both to verify that the 
full demand can be met.   
  

  
For a future testing program, probably something specialized would be needed. 
Make sure it is available in writing.   
  
  
  
  
  
  
  

  
  
>   
> On Jan 29, 2024 at 11:45 AM,  <Craig Prahl (mailto:[email protected])>  
> wrote:
>   
>   
>         
>   
>
> I have a project that requires two 1500 gpm pumps to meet the most demanding 
> system requirements.      Client doesn’t want any pumps over 1500 gpm.    
> Long story.
>
>   
>
>   
>
>   
>
> As far as testing, would you test each pump individually or together or    ??
>
>   
>
>   
>
>   
>
> Trying to establish what we need as far as a test header.   
>
>   
>
>   
>
>   
>
> Thanks.
>
>   
>
>   
>
>   
>   
>
>  Craig Prahl   |Jacobs     | Fire Protection SME – Special Hazards |      
> [email protected] (mailto:[email protected])|www.jacobs.com 
> (https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$)
>
>   
>
> 1041 East Butler Road      Greenville, South Carolina    29606   
>
>   
>
> CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS
>
>   
>
>   
>
>   
>   
>   
>     
>  NOTICE - This communication may contain confidential and privileged 
> information that is for the sole use of the intended recipient. Any viewing, 
> copying or distribution of, or reliance on this message by unintended 
> recipients is strictly prohibited. If you have received this message in 
> error, please notify us immediately by replying to the message and deleting 
> it from your computer.
>  _________________________________________________________ SprinklerForum 
> mailing list: 
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> To unsubscribe send an email to [email protected]  
>           
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to