*Bob Caputo, CFPS*

*President*

*American Fire Sprinkler Association*

c:     760-908-7753

p:

214-349-5965 ext124

w:

firesprinkler.org

<https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/afsa/status/1039528345367732224>
<https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
   <https://www.instagram.com/firesprinklerorg/>



*Treat Your Apprentices Like VIPs!*

AFSA’s Virtual Instruction Program (VIP) for Apprentices is training that
comes straight from our expert instructors. They lead the way to ensure
your men and women are trained, letting you focus on OJT. Click here
<https://www.firesprinkler.org/sprinkler-apprentice-training/> to learn
more and enrol



*From:* mattgrise5 <[email protected]>
*Sent:* Saturday, January 27, 2024 11:49 AM
*To:* Discussion list on issues relating to automatic fire sprinklers <
[email protected]>
*Subject:* [Sprinklerforum] Sprinkler age magazine.



I was just sitting down to read the December issue of sprinkler age and I
hope that everyone has had a chance to take in the outstanding update to Mr
Caputo's picure with the President's Report (pg8). We may need to consider
his portrait artist for the Parmlee Award! Very regal!  :)







Sent from my T-Mobile 5G Device





-------- Original message --------

From: Jackie Ward <[email protected]>

Date: 1/24/24 10:16 PM (GMT-06:00)

To: Discussion list on issues relating to automatic fire sprinklers <
[email protected]>

Subject: [Sprinklerforum] Re: Refill mechanism for a break tank (NFPA 22)



With your break tank capacity exceeding a 30 minute duration, that is the
way I would interpret it.  Depending on your available water supply, you
may have to increase your break tank size in order for your required refill
rate to be less than your available refill rate.







Sincerely;



Jackie "JW" Ward; SET

1-405-240-7076

[email protected]

NICET  IV Cert. No. 104187

Victaulic Vortex Integrator



Firetrol Protection Systems

108 NW 132nd Street; Oklahoma City, OK 73114

405-752-2330  Ext. 10230  Fax:405-752-2297

License No: AR-FSS-162, LA-F415, OK-863 & 302, TX - ECR-1751432,
ACR-1751168, SCR-G-0292



[image: Firetrol Oklahoma City BACK]





*From:* Daniel Bobadilla <[email protected]>
*Sent:* Wednesday, January 24, 2024 9:47 PM
*To:* Discussion list on issues relating to automatic fire sprinklers <
[email protected]>
*Subject:* [Sprinklerforum] Refill mechanism for a break tank (NFPA 22)



Hello guys, hoping you're doing great!



I am designing a sprinkler system for a warehouse, but the pressure from
the city water main is to weak to deliver the required pressure to the
system, so the client wants to install a booster pump with a break tank.



The break tank is sized to provide a duration of 30 minutes of the maximum
system demand (1282 gpm), this is 38,500 gallons aprox. The issue is how to
calculate the refill mechanism.



NFPA 22-2018 sec. 14.5.2.2.1 states "*The refill mechanism shall be
designed for and capable of refilling the tank at 110 percent of the rate
required to provide the total fire protection system demand [110% (Total
Demand – Tank Capacity) / Duration]."*



In terms of system demand (1282 gpm for 120 minutes according to a CMDA
sprinkler system = 153,840 gallons) I made the following calculation:



110% (153,840 gal - 38,500 gal) /120 min = 1,057 gpm.



The refill mechanism shall be capable of providing a flow of 1,057 gpm to
fill the tank while the fire pump is operating at system demand.



Am I right?



Bless to all of you!



-- 

=?Este mensaje se dirige exclusivamente a su destinatario y puede contener
información privilegiada o confidencial. Si no es Ud. el destinatario
indicado, queda notificado de que la utilización, divulgación y/o copia sin
autorización está prohibida en virtud de la legislación vigente. Si ha
recibido este mensaje por error, le rogamos que nos lo comunique
inmediatamente por esta misma vía y proceda a su destrucción.


This message is intended exclusively for its addressee and may contain
information that is confidential and protected by professional privilege.
If you are not the intended recipient you are hereby notified that any
dissemination, copy or disclosure of this communication is strictly
prohibited by law. If this message has been received in error, please
notify us immediately via e-mail and delete it.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to