Hello guys, hoping you're doing great!

I am designing a sprinkler system for a warehouse, but the pressure from
the city water main is to weak to deliver the required pressure to the
system, so the client wants to install a booster pump with a break tank.

The break tank is sized to provide a duration of 30 minutes of the maximum
system demand (1282 gpm), this is 38,500 gallons aprox. The issue is how to
calculate the refill mechanism.

NFPA 22-2018 sec. 14.5.2.2.1 states "*The refill mechanism shall be
designed for and capable of refilling the tank at 110 percent of the rate
required to provide the total fire protection system demand [110% (Total
Demand – Tank Capacity) / Duration]."*

In terms of system demand (1282 gpm for 120 minutes according to a CMDA
sprinkler system = 153,840 gallons) I made the following calculation:

110% (153,840 gal - 38,500 gal) /120 min = 1,057 gpm.

The refill mechanism shall be capable of providing a flow of 1,057 gpm to
fill the tank while the fire pump is operating at system demand.

Am I right?

Bless to all of you!

-- 
=?Este mensaje se dirige exclusivamente a su destinatario y puede contener
información privilegiada o confidencial. Si no es Ud. el destinatario
indicado, queda notificado de que la utilización, divulgación y/o copia sin
autorización está prohibida en virtud de la legislación vigente. Si ha
recibido este mensaje por error, le rogamos que nos lo comunique
inmediatamente por esta misma vía y proceda a su destrucción.


This message is intended exclusively for its addressee and may contain
information that is confidential and protected by professional privilege.
If you are not the intended recipient you are hereby notified that any
dissemination, copy or disclosure of this communication is strictly
prohibited by law. If this message has been received in error, please
notify us immediately via e-mail and delete it.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to