What Craig said and more.   The rule in CA is that a building must be 
maintained in accordance with codes and standards in effect when it was first 
permitted for occupancy.   If this is an office building and was first 
certified for B Occupancy, and has been continuously used for Group B, and the 
new tenancy is classified as Group B, then a retrofit is not required by code, 
unless there are extenuating circumstances.  F’rinstance, does the mezzanine 
meet travel distance requirements?

But it sounds like you’re describing a single tenant in a building that is 
20,000 sq. ft. including said office/mezz, which leaves 13,000 sq. ft. of… 
storage perhaps?    If the building is an unsprinklered S-1, it may still be 
grandfathered if the new tenant is S-1.   But if it’s Group F (as Craig alluded 
to), and they want to store in the high-bay portion, then it’s a change of use 
and the building official is specifically empowered by CBC to throw the new 
book at it.   And since you’re in LACFD jurisdiction, there may very well be a 
bureau policy regarding changes of tenancy, use, etc.

The determination of whether a permit requires sprinklers shouldn’t be in your 
scope unless you’ve been tasked with it as the sprinkler contractor.   The 
architect and owner need to determine whether a retrofit provision in the code 
is applicable to this project prior to submission for approval of the general 
building permit.

Steve L.

From: George Medina Jr. <[email protected]>
Sent: Thursday, January 18, 2024 10:11 AM
To: Discussion List On Issues Relating To Automatic Fire Sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Non Sprinklered Building Retrofit in California

There is a 20,000 sq. ft. building with 7,000 sq. ft. of office & mezzanine 
(About 17' high).
The building is not sprinklered and vacant. New tenant (Our Client) wants to 
occupy with the same occupancy (no change in occupancy). Would they need to put 
sprinklers? It is located in Marina Del Ray (LA County). Where would it address 
it in the 2022 CBC or CFC, or any LA County regulations?

Thanks for any Inputs,

George Medina Jr.
Sr. Fire Sprinkler Designer
SINGLETON FIRE PROTECTION INC.