I made up a laminated sign to hang on the dry valve.

Thank you,

Brian Harris, CET
BVS Systems Inc.

From: Bob Caputo <[email protected]>
Sent: Wednesday, January 3, 2024 8:04 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Dry System Aux. Drain

Brian,

Anything you can do to ensure the drum drips are attended to at the onset and 
during cold weather will be a benefit.  It’s the owners responsibility, so 
educating them will be the best way.

That said,  NFPA 13 section 29.6.1 requires the installing contractor to 
provide a general information sign….

The sign shall include the following information:  (14)  Location of auxiliary 
drains and low point drains on dry pipe and preaction systems

So, assuming the signage required on the riser since the 1999 or 2002 code 
cycle is there, I’m not sure another sign will help.



[https://www.dropbox.com/s/g4h8r7hdtsr6154/AFSA_L.png?raw=1]
Bob Caputo, CFPS
President
American Fire Sprinkler Association
c:     760-908-7753
p:
214-349-5965 ext124
w:
firesprinkler.org<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2ffiresprinkler.org%2f&c=E,1,S0KFlWuFiUE9c_aNydHsvuKF2h5oWKPb5CCtyDL3jmYf641rrANqQBCu14rbEv4lLUAlaM6_Kzt-8yOFNUJ6mZCTR7LApBt_Z74KYyXtNDHrLsvh&typo=1>
[http://cdn2.hubspot.net/hubfs/184235/dev_images/signature_app/facebook_sig.png]<https://www.facebook.com/firesprinkler.org/>
  
[http://cdn2.hubspot.net/hubfs/184235/dev_images/signature_app/twitter_sig.png] 
<https://twitter.com/afsa/status/1039528345367732224>   
[http://cdn2.hubspot.net/hubfs/184235/dev_images/signature_app/linkedin_sig.png]
 <https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>  
 
[http://cdn2.hubspot.net/hubfs/184235/dev_images/signature_app/instagram_sig.png]
 <https://www.instagram.com/firesprinklerorg/>


From: Brian Harris <[email protected]<mailto:[email protected]>>
Sent: Wednesday, January 3, 2024 6:57 AM
To: 
[email protected]<mailto:[email protected]>
Subject: [Sprinklerforum] Dry System Aux. Drain

I have a dry attic system where in addition to a couple drum drips I also have 
(2) aux. drains per 8.16.2.5.3.3 (2016). What’s the best way to make sure these 
get drained before the system is put into service? I’m thinking of making an 
8.5x11 laminated print to put on the dry riser and note these (2) locations. 
Thoughts?

Thank you,

Brian Harris, CET
BVS Systems Inc.
bvssystemsinc.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fbvssystemsinc.com%2f&c=E,1,vM0yO2CuOq-CaN99-2VtQml-AaXaYJvzX8_ytxctWOlY2efJPyhTJiOkRD6CIJnRQtnD466I9g_6uL33FGoeODh9s0hGWy36E4ZslF3mJ_XBnsx9&typo=1>
Phone: 704.896.9989
Fax: 704.896.1935

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to