Todd-
Thank you! You can lead a horse to water……

Thank you,

Brian Harris, CET
BVS Systems Inc.

From: Fpdcdesign <[email protected]>
Sent: Wednesday, January 3, 2024 8:24 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Dry System Aux. Drain

Brian, what I have seen is a chart with the location of the low points mounted 
near the riser. Also bright orange tags on the drain valves themselves to make 
them a little easier to spot. Best you can do it say that they exist and here 
is where they are.

I’m not sure what happens in 704, but out here General Information Signs are as 
rare as Owner’s Information Certificates. I wouldn’t count on anyone paying 
attention.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080<tel:860-535-2080> (ofc)
860-554-7054<tel:860-554-7054>  (fax)
860-608-4559<tel:860-608-4559> (cell)



On Jan 3, 2024 at 7:58 AM, <Brian Harris<mailto:[email protected]>> 
wrote:
I have a dry attic system where in addition to a couple drum drips I also have 
(2) aux. drains per 8.16.2.5.3.3 (2016). What’s the best way to make sure these 
get drained before the system is put into service? I’m thinking of making an 
8.5x11 laminated print to put on the dry riser and note these (2) locations. 
Thoughts?

Thank you,

Brian Harris, CET
BVS Systems Inc.
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

_________________________________________________________ SprinklerForum 
mailing list: 
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To 
unsubscribe send an email to 
[email protected]<mailto:[email protected]>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to