Brian, what I have seen is a chart with the location of the low points 
mounted near the riser. Also bright orange tags on the drain valves themselves 
to make them a little easier to spot. Best you can do it say that they exist 
and here is where they are.   
  

  
I’m not sure what happens in 704, but out here General Information Signs are as 
rare as Owner’s Information Certificates. I wouldn’t count on anyone paying 
attention.
  
  
  
Todd G Williams, PE  
Fire Protection Design/Consulting
  
Stonington, CT
  
860-535-2080 (tel:860-535-2080)  (ofc)
  
860-554-7054 (tel:860-554-7054)     (fax)
  
860-608-4559 (tel:860-608-4559)  (cell)
  
  
  
  

  
  
>   
> On Jan 3, 2024 at 7:58 AM,  <Brian Harris (mailto:[email protected])> 
>  wrote:
>   
>   
>         
>   
>
> I have a dry attic system where in addition to a couple drum drips I also 
> have (2) aux. drains per 8.16.2.5.3.3 (2016). What’s the best way to make 
> sure these get drained before the system is put into service? I’m thinking of 
> making an 8.5x11 laminated print to put on the dry riser and note these (2) 
> locations. Thoughts?
>
>   
>
>   
>
>   
>