Micah,
When you test the valves you will test each one individually flowing 250
gpm so therefore you have to size them individually.

On Tue, Oct 31, 2023 at 5:53 AM Micah Davis <[email protected]> wrote:

> Good morning, Forum!  I hope everyone is having a great week!!
>
> I think I got this right, but someone is questioning me.  I have an
> automatic standpipe with factory pressure-regulating valves (i.e., Zurn
> 4000).  When calculating residual pressures at the inlet of the PRV to be
> used in the sizing charts, the question is, how much water should I be
> flowing in the system?  One suggestion is only flowing 250 gpm at the hose
> valve you are sizing.  The other suggestion is flowing the system demand
> flow per NFPA 14.  In this case, that would be 750 gpm (250 gpm at each of
> the two most remote hose valves plus 250 gpm at the top of the only other
> standpipe).  We are in agreement that the calculation should be a source
> calc to determine the actual pressure provided by the system.
>