Mike - thanks for the response!

I was thinking that (2016) 8.15.6 was referring to platforms that are low
to the ground that you could not really walk under.

The examples I have seen would have met the exemption for 8.15.7.2 (totally
non-combustible, no storage)

On Thu, Oct 26, 2023 at 12:17 PM Mike Klingler <
[email protected]> wrote:

> NFPA 13 (2016) 8.15.6 or 8.15.7.
>
>
>
> *Michael Klingler, CET*
>
> NICET #: 161423
>
> Designer/Project Manager
>
> Precision Fire Protection, Inc.
>
> 97 Mechanic Street | Reinholds, PA 17569
> O: 717.484.2642 | M: 717.202.7327
>
> *[email protected] <[email protected]>* | 
> *www.precisionfirepro.com
> <http://www.precisionfirepro.com/>*
>
> [image: PFPI Logo Final-small]
>
>
>
> *From:* Matt Grise <[email protected]>
> *Sent:* Thursday, October 26, 2023 1:09 PM
> *To:* [email protected]
> *Subject:* [Sprinklerforum] canopy with occupancy above
>
>
>
> I often see requests/requirements to protect under canopies that would
> normally be excluded by NFPA 13 due to the fact that they have occupancy
> above.
>
>
>
> for example - a non-combustible canopy with no storage, that has chairs on
> top of it (assembly space). or a second story that extends out farther than
> the footprint of the first story.
>
>
>
> Is there a code requirement for this? Is it just something that people
> have become used to doing? I have looked around and I just can't find it!
>
>
>
> Thanks!
>
>
>
> Matt
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to