2013 edition of NFPA 13, 9.3.6.6,  Sprigs 4’-0 or longer shall be restrained….

 

Regards,

G. Tim Stone

 

G. Tim Stone Consulting, LLC

NICET Level III Engineering Technician

Fire Protection Sprinkler Design

and Consulting Services

 

   117 Old Stage Rd. - Essex Jct., VT. 05452

                 CELL: (802) 373-0638  

             [email protected] <mailto:[email protected]> 

 

From: Jeff Werre <[email protected]> 
Sent: Thursday, October 19, 2023 12:58 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>; George Medina Jr. 
<[email protected]>
Subject: [Sprinklerforum] Re: 1" Armover Restraint

 

Where does the requirement to brace a sprig up at 4 feet come from? 

 

Thank you-

 

Jeff Werre, CFM  

Plan Review and Inspection Specialist

 

Development Services

City of Goodyear, Arizona

1900 North Civic Square

Goodyear, AZ 85395

 

c 602 316-0704

 w goodyearaz.gov <http://www.goodyearaz.gov/> 

e  <mailto:[email protected]> [email protected]

 

The Accela Citizen Access portal (ACA) is coming to the City of Goodyear.

The new permit software implementation is planned for Early 2024!

Visit the  <https://www.goodyearaz.gov/business/development-center> Development 
Center for Resources and Access to the Electronic Plan Review (EPR) system.

If you need technical assistance, send an email to  
<mailto:[email protected]> [email protected]

 

 

From: Bob Caputo <[email protected] <mailto:[email protected]> 
> 
Sent: Thursday, October 19, 2023 9:41 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected] 
<mailto:[email protected]> >; George Medina Jr. 
<[email protected] <mailto:[email protected]> >
Subject: [Sprinklerforum] Re: 1" Armover Restraint

 

⚠ This email arrived from an external source - Please exercise caution when 
opening any attachments or clicking on links 

 

George, 

 

An arm over to a single sprinkler is defined as an arm over whereas when two 
sprinklers are served, it’s considered a branch line. Branch lines require 
restraint. If the arm over is to a sprig up longer that 4ft, the sprig requires 
restraint. 

 

I am not aware of a requirement to restrain the arm over (but if it’s long 
enough….) 

 

I’m sitting in an airport without a book so there might be other opinions 

 

Bob Caputo

 

On Thu, Oct 19, 2023 at 11:35 AM George Medina Jr. <[email protected] 
<mailto:[email protected]> > wrote:

I have an armover that is 2'-4" in length. The SEOR is requiring me to put a 
diagonal brace on the branch line that the armover is supplied from and a 
restraint on the armover ( I had left a branchline restraint detail from my 
template and I probably should not have left it on with these small aromovers) 
When is an armover required to be restrained (if at all?). Could not find any 
specific length in NFPA-13 (2016 ed.)  

 

 

George Medina Jr.

Sr. Fire Sprinkler Designer

SINGLETON FIRE PROTECTION INC.

Office: (818) 252-5744

Cell: (323) 906-5701
Business Hours: 9:00am-5:00pm

 


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected] 
<mailto:[email protected]> 

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to