George,

An arm over to a single sprinkler is defined as an arm over whereas when
two sprinklers are served, it’s considered a branch line. Branch lines
require restraint. If the arm over is to a sprig up longer that 4ft, the
sprig requires restraint.

I am not aware of a requirement to restrain the arm over (but if it’s long
enough….)

I’m sitting in an airport without a book so there might be other opinions

Bob Caputo

On Thu, Oct 19, 2023 at 11:35 AM George Medina Jr. <
[email protected]> wrote:

> I have an armover that is 2'-4" in length. The SEOR is requiring me to put
> a diagonal brace on the branch line that the armover is supplied from and a
> restraint on the armover ( I had left a branchline restraint detail from my
> template and I probably should not have left it on with these small
> aromovers) When is an armover required to be restrained (if at all?). Could
> not find any specific length in NFPA-13 (2016 ed.)
>
>
> George Medina Jr.