If/when an applicable standard such as NFPA 86 tells you that no fire 
sprinklers are required within the oven, no sprinklers are required within and 
no "compensation" in the overhead is required unless it states so.

You look at the overall area and the hazards present and then make the decision 
on the appropriate criteria to apply.  Is there an appreciable amount of 
combustibles on the floor?


Craig Prahl | Jacobs | Fire Protection SME - Special Hazards | 
[email protected]<mailto:[email protected]> | 
www.jacobs.com<https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$>
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS

From: Taylor Schumacher <[email protected]<mailto:[email protected]>>
Sent: Thursday, October 5, 2023 12:48 PM
To: '[email protected]' 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Paint Line-Furnaces

I have a paint line for simple metal trailers and components. I know how to do 
the non-automated powder booths easy enough. What I am struggling with is other 
"booths" on the line. Blast furnaces, in particular, for drying post wash and 
for curing the powder coated parts. They are approximately 1,000 sq. ft. 
rectangles and 20 foot tall. These furnaces regularly get to 650 °F. I don't 
need protection inside per NFPA 86 and the IFC requirements.

When my brain switches back to 13 requirements, I have a large obstructed area 
shielding concrete and transitory metal frames. Insurance is recommending OH2 
overhead for this area. Do I need to increase my overhead requirements to EH2 
for shielded fires even though they're not "combustible" shielded fires?

Any thoughts would be appreciated.


Taylor Schumacher


________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to