Thank you for the response, Steve!  Does the redundant fill valves for the
tank satisfy the secondary supply requirement of the IBC without an
additional tank?  I was interpreting the city main connected to the pump as
the primary supply and the tank as the secondary supply (or vice versa).
If my interpretation is wrong and the tank with redundant fill valves meets
BOTH the primary and secondary water supply requirements, I can NOT connect
the city water main to the fire pump, and the problem is solved using your
method above.

Am I tracking correctly?

My thought is that if the city main stays connected to the pump and my
demand calcs and PRV settings are based on the supply from the tank (which
I think is correct), how do we avoid overpressurization with the added
pressure from the city?  I'm probably overthinking this somewhere!  That
tends to be my M.O.!

Micah Davis

Ferguson Fire Design

[email protected]


On Mon, Sep 25, 2023 at 12:02 PM Steve Leyton <[email protected]>
wrote:

> Micah:
>
> The best way to stabilize the pump discharge pressure and give yourself a
> (nearly) straight line suction pressure curve is to arrange the required
> secondary water supply as a break tank.   Fill the tank with city water
> (recommend to manifold at least one automatic plus one manual fill; in my
> neck of the woods we use two automatic and one manual) and base  your
> calculations on the lowest potential water level in the tank.  We simply
> use the pump’s performance curve as a water supply assuming 0 psi suction
> head.   Depending on water column height, your actual discharge pressure
> variation will be  ≤ 5 psi, unless the tank is uniquely configured and
> multi-story.
>
>
>
>
>
> The foregoing is my opinion only and does not represent NFPA or the NFPA
> 14 Technical Committee, nor intended to serve as an interpretation of the
> standard.
>
>
>
> *Protection Design and Consulting*
>
> Steve Leyton, President
>
> T  *|*  619.255.8964 x 102  *| *
> *www.protectiondesign.com <http://www.protectiondesign.com/> *2851 Camino
> Del Rio South  *|*  Suite 210  *|*  San Diego, CA  92108
> Fire Protection System Design *|* Consulting *|* Planning *|* Training
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
> *From:* Micah Davis <[email protected]>
> *Sent:* Monday, September 25, 2023 8:55 AM
> *To:* SprinklerForum <[email protected]>
> *Subject:* [Sprinklerforum] Standpipe PRV Question
>
>
>
> Good morning, Forum!
>
>
>
> I've got a head-scratcher and am interested in the Forum's collective
> opinion!  Important project parameters are as follows.
>
>
>
> - 42-story high rise with an automatic standpipe
>
> - Seismic Design Category - C
>
> - IBC 2018
>
> - Fire pump supplied by city water supply
>
> - Secondary supply, as required by IBC 403.3.3, is a tank of adequate size
>
> - 305 psi @ 1000 gpm pump sized based on the feed from tank
>
> - Direct-acting pressure reducing valves on each floor
>
>
>
> Here is my issue.  If I base my PRV settings on city supply, I cannot get
> 100 psi at the remote valves when calculating tank as supply.  If I base my
> PRV settings on tank supply, I am over 175 psi discharge on the valve when
> calculating city as supply.  If I try to get my settings using the city as
> static and the tank as residual pressures, there is no PRV setting that
> works.
>
>
>
> I have my opinions about what I think should happen here, but I want to
> see what the Forum thinks.  I will not bother the group with what the
> design team is suggesting I do.
>
>
>
> Micah Davis
>
> Ferguson Fire Design
>
> [email protected]
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>