Good morning, Forum!

I've got a head-scratcher and am interested in the Forum's collective
opinion!  Important project parameters are as follows.

- 42-story high rise with an automatic standpipe
- Seismic Design Category - C
- IBC 2018
- Fire pump supplied by city water supply
- Secondary supply, as required by IBC 403.3.3, is a tank of adequate size
- 305 psi @ 1000 gpm pump sized based on the feed from tank
- Direct-acting pressure reducing valves on each floor

Here is my issue.  If I base my PRV settings on city supply, I cannot get
100 psi at the remote valves when calculating tank as supply.  If I base my
PRV settings on tank supply, I am over 175 psi discharge on the valve when
calculating city as supply.  If I try to get my settings using the city as
static and the tank as residual pressures, there is no PRV setting that
works.

I have my opinions about what I think should happen here, but I want to see
what the Forum thinks.  I will not bother the group with what the design
team is suggesting I do.