Both structures are steel construction, roof is steel deck, steel open girders 
and joists. Mezzanine is steel beams, open grating, and steel plate for 
walkways.

I’m not questioning if sprinklers are needed, I agree they are, I am 
questioning if they need to be ESFR to match the overhead or they can be 
different (CMDA, etc..)


Joe
Burtell | SET, CFPS
Fire Sprinkler Manager
D
C


406-204-4653
406-861-4507
From: Prahl, Craig <[email protected]>
Sent: Tuesday, August 29, 2023 9:28 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: ESFR Below Mezzanine


CAUTION: This email originated from outside the organization. Do not follow 
guidance, click links, or open attachments unless you KNOW the content is safe.
A mezzanine is an obstruction to overhead sprinklers. Of that there is no doubt.

Sprinklers need to be provide under the mezzanines as noted in the cited NFPA 
13 section.

Craig Prahl | Jacobs | Fire Protection SME – Special Hazards | 
[email protected]<mailto:[email protected]> | 
www.jacobs.com<https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$>
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS


From: Joe Burtell [MT-BILL] 
<[email protected]<mailto:[email protected]>>
Sent: Tuesday, August 29, 2023 9:23 AM
To: 
[email protected]<mailto:[email protected]>
Subject: [EXTERNAL] [Sprinklerforum] ESFR Below Mezzanine

I have a soda manufacturing warehouse with ESFR at the roof deck. They are 
building out some mezzanines in the middle of the warehouse that will have 
bottling equipment.  The engineer is requiring that below the mezzanine have 
ESFR per NFPA 13 2019 9.5.5.3.3. I am questioning if the mezzanine is really 
treated like an obstruction? I think it would be treated like in-racks would 
and have its own design based on what’s under the mezzanine.

[cid:[email protected]]
Joe​

Burtell | SET, CFPS
Fire Sprinkler Manager
D
C


406-204-4653<tel:406-204-4653>
406-861-4507<tel:406-861-4507>
3004 1st Ave South
Billings
,
MT
 59101
Office:
406‑652‑7697
www.summitfiresecurity.com<https://urldefense.com/v3/__http:/www.summitfiresecurity.com__;!!B5cixuoO7ltTeg!FzWefsxguMXLMMbjMLpaQSGEn8ZDKtVk8zEzI6o24UsVewq_MXB3dLkqQtmzX2oDwKQ3aaFkX2W0zPKniNKj8Sfkax49$>
This information transmitted, including attachments, is intended only for the 
person(s) or entity to which it is addressed and may contain confidential 
and/or privileged material. Any review, retransmission, dissemination or other 
use of, or taking of any action in reliance upon this information by persons or 
entities other than the intended recipient is prohibited. If you received this 
in error, please contact the sender and destroy any copies of this information.


________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to