Arguably you’re performing an NFPA 25 action, replacing antifreeze.  NFPA 25 
2023: 5.3.4.4.1 Where used to replace nonlisted antifreeze solutions, listed 
antifreeze solutions shall be permitted to be used outside their listing 
limitations, provided the temperature range limitations are not exceeded.

The annex material goes on to detail the volume limits and/or calc requirements 
can be ignored.  The logic is that the new antifreeze is less flammable than 
the old, so spraying it on a fire is more effective until water arrives than 
the old antifreeze anyway, at least by my reading and paraphrasing of the annex.

Mike Morey
CFPS 3229 • NICET S.E.T. 123677
Project Manager • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive • Fort Wayne, IN • 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]
[cid:[email protected]]

From: Matt Grise <[email protected]>
Sent: Friday, August 25, 2023 4:40 AM
To: [email protected]
Subject: [Sprinklerforum] antifreeze change out

We have come across an antifreeze system that has not been serviced in a while 
and have been asked to replace the old (non-listed) glycol antifreeze with 
listed antifreeze per NFPA 25. The system definitely exceeds 40 gallons, so any 
calculations
ZjQcmQRYFpfptBannerStart
This Message Is From an External Sender
This message originated outside your organization.
ZjQcmQRYFpfptBannerEnd
We have come across an antifreeze system that has not been serviced in a while 
and have been asked to replace the old (non-listed) glycol antifreeze with 
listed antifreeze per NFPA 25.

The system definitely exceeds 40 gallons, so any calculations on it should be 
done as darcy-weisbach.

I feel like I saw somewhere that you are allowed to just swap out old 
non-listed antifreeze with listed antifreeze without performing hydraulic 
calculations using the properties of the new antifreeze - that they are close 
enough. However, I cannot seem to find where that is actually written down.

Does that ring a bell with anyone? Am I mis-remembering?

Thanks!

Matt Grise

This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to