The intent is to calculate the 4 most demanding sprinklers that would
activate in a single fire event, therefore we tend to submit the version
that reflects that scenario but we typically prove the calcs for our sake.

On Thu, Jul 20, 2023 at 11:07 AM Brett Peters <[email protected]> wrote:

> LOL, unfortunately I have someone arguing that it can be done the other
> way because "those heads have a larger area of coverage".
> In my opinion they are twisting the definitions of "adjacent" and
> "hydraulically most demanding" to include the sprinklers that cover the
> largest area but in my opinion the largest floor space doesn't
> necessarily present as the most demanding.
>
> I will be on Holidays from August 12th to 21st, returning to work on
> Tuesday August 22nd
>
> Thanks
>
> Brett Peters
> General Manager Installation & Design
> Proudline Fire Protection Services Ltd.
> [email protected]
> 780 490 7602 office ext 202
> 780 490 7605 fax
> 780 777 0568 cell
> 780 718 2676 24h
> Visit us at www.proudline.ca
>
> Proudline now offers ULc listed monitoring services, please contact
> [email protected] for more information
>
>
>
>
>
>
> On Thu, Jul 20, 2023 at 9:31 AM Chris Dorn <
> [email protected]> wrote:
>
>> Brett,
>>
>> I think you answered your own question. “I always choose whatever gives
>> me the greatest pressure loss not necessarily the larger flow.” Wouldn’t
>> that by definition be the hydraulically most demanding area regardless of
>> location? It’s exactly what I do also in this situation.
>>
>> Chris Dorn
>>
>>
>>
>>
>>
>>
>>
>> *From:* Brett Peters <[email protected]>
>> *Sent:* Thursday, July 20, 2023 11:15 AM
>> *To:* Sprinklerforum <[email protected]>
>> *Subject:* [Sprinklerforum] Residential Design in NFPA 13
>>
>>
>>
>> Having a debate on which sprinklers actually have to be part of the
>> hydraulic calculation in a residential unit in a 13 building (So the
>> calculation has to include 4 sprinklers) - NFPA 13, 2013
>>
>>
>>
>> 11.3.1.1* The design area shall be the area that includes the four
>> adjacent sprinklers that produce
>>
>> the greatest hydraulic demand.
>>
>>
>>
>> With 11.3.1.1 in mind if you have a space where you have less than 4
>> sprinklers in a compartment and you have to start adding sprinklers in
>> other compartments to come up with 4 in the calculation, what is the method
>> that you have to use?
>>
>> So for arguments sake this scenario is 2 sprinklers in one compartment
>> and then two "adjacent" sprinklers outside of that compartment but there
>> are sprinklers in different directions that can be considered as "adjacent"
>>
>>    1. Adding sprinklers from the next compartment on a different
>>    sprinkler line which would qualify as an "adjacent sprinkler" and
>>    potentially have 4 sprinklers fed form 3 different lines or
>>    2. adding "adjacent sprinklers" that are first on a common sprinkler
>>    line and potentially having 3 sprinklers on a single line.
>>
>> My argument is that scenario 2 has to be followed as that would produce
>> the largest demand to a sprinkler line and if required increase the size of
>> that line.
>>
>> The other argument is that in scenario 1 they are picking the "adjacent
>> sprinkler" that has a larger protection area, so the actual water flow
>> might be slightly higher but it spreads the flow through 3 different lines
>> instead of only 2
>>
>>
>>
>> So scenario 1 has more flow but less pressure loss resulting in smaller
>> piping and scenario 2 has less flow but more pressure loss requiring larger
>> pipe to be installed.
>>
>>
>>
>> So what are other people doing in these situations and what is really
>> considered as producing the greatest hydraulic demand? I always choose
>> whatever gives me the greatest pressure loss not necessarily the larger
>> flow.
>>
>>
>>
>> I will be on Holidays from August 12th to 21st, returning to work on
>> Tuesday August 22nd
>>
>>
>>
>> Thanks
>>
>>
>>
>> Brett Peters
>>
>> General Manager Installation & Design
>>
>> Proudline Fire Protection Services Ltd.
>>
>> [email protected]
>>
>> 780 490 7602 office ext 202
>>
>> 780 490 7605 fax
>>
>> 780 777 0568 cell
>>
>> 780 718 2676 24h
>>
>> Visit us at www.proudline.ca
>>
>>
>>
>> Proudline now offers ULc listed monitoring services, please contact
>> [email protected] for more information
>>
>>
>>
>>
>>
>>
>>
>>
>>
>> _________________________________________________________
>> SprinklerForum mailing list:
>>
>> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
>> To unsubscribe send an email to
>> [email protected]
>>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]



-- 

Greg McGahan

*Genesis Fire Services, LLC*

*4912 Glover Lane. Milton, FL **32570*

*P- 850-637-8535*

*C- 850-712-9555*
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to