You measure from the centerline of the offending elbow (the one in the 
direction you aren’t allowed to go) to the pump suction flange and you need 
those 10 pipe diameters, but you can go up or down as many times as you want to 
get the required length, as long as all the elbows you are measuring through 
are in the allowed direction.

-Kyle M

From: Fpdcdesign <[email protected]>
Sent: Friday, July 14, 2023 11:07 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [EXTERNAL] [Sprinklerforum] Re: Elbows in pump suction

Eric, My main question is if the 10 diameter requirement can be split into 2 
section or does it have to be one continuous length?

The problem is that the suction pressure on the pump test goes to 0 psi at 1500 
gpm. Based on my calculations, it should be around 17 psi. I know what you are 
all thinking; we are below 20 psi and this pump is never going to flow 2250 
gpm. Correct. This pump was oversized and installed in an undersized pump house 
as required by the Engineer. According to him, our job is to “make their design 
work and no substitutions are allowed”. Fortunately the system demand is about 
1200 gpm so we may eventually be able to meet that demand.

This is. 6 month cluster f*** that has been going on for 2-1/2 years.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080<tel:860-535-2080> (ofc)
860-554-7054<tel:860-554-7054>  (fax)
860-608-4559<tel:860-608-4559> (cell)



On Jul 14, 2023 at 1:05 PM, <Eric Rieve<mailto:[email protected]>> wrote:
Todd,

Like Brett mentioned, going vertical to eat up pipe length is shown in the 
annex of NFPA 20, and I’ve seen/used that approach before. When you say there 
is a problem with the test, is this for a new fire pump installation? Are you 
not meeting your curve, and if so, are you off by a substantial amount?

I was always under the impression that the un-balanced flow caused by the elbow 
being to close to the suction inlet was a “long-term, causes damage over time” 
sort of issue, so if your problem is on a new install, I’d want to double check 
that there isn’t some other cause. 38” of straight run obviously isn’t great or 
to code, but it’s not like the elbow is directly attached to the suction flange 
either.

Backflow has OS&Y valves right?

Hope this helps,
Eric Rieve
Rieve Fire Protection

From: Fpdcdesign <[email protected]<mailto:[email protected]>>
Sent: Friday, July 14, 2023 12:37 PM
To: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Elbows in pump suction

I am working on a pump house that has a 1500 gpm pump with an 8” suction line 
(no reducer). There is an elbow in the suction line parallel to the pump shaft 
with a piece of pipe that is 38” from the suction flange and there is a problem 
with the test. We have to add another 42” from the parallel elbow to the 
flange. There is physically not enough room in the pump house to make it in a 
single straight run. My proposal is to turn the offending elbow looking up (so 
no linger parallel), add a 42” vertical piece to an elbow and pipe that back to 
the discharge from the backflow preventer. Can the 80” be split into 2 pieces? 
NFPA 20 says nothing about that but I was wondering how it works in real life.

FYI, the backflow discharge is already over the 80” threshold.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080<tel:860-535-2080> (ofc)
860-554-7054<tel:860-554-7054>  (fax)
860-608-4559<tel:860-608-4559> (cell)
_________________________________________________________ SprinklerForum 
mailing list: 
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To 
unsubscribe send an email to 
[email protected]<mailto:[email protected]>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to