It was my understanding that the arm over requirements were to mitigate the 
increased jet effect of  the sprinkler at high pressure. I would imagine that 
the bracket for the flex drop would control that issue. As long as they are 
rated for the pressure you want.

Matt

From: [email protected] <[email protected]>
Sent: Thursday, May 11, 2023 11:41 AM
To: [email protected]
Subject: [Sprinklerforum] Flex Drops in excess of 100psi

Having an internal discussion, and the thought came up..,

Are there any discussions or considerations on the reduced arm over length when 
pressure is above 100psi?

In other words, since the common flex fittings are rated to 175psi in a 
bracket, attached to a ceiling assembly, can we go to 36" for 1" with more than 
100psi at the sprinkler?

I know as written you cannot. But was wondering if this had been brought up.

R/
Matt