If we’re talking “hard pipe” portion of the arm over, we stick with the 2’ <100 
1’ >100 rule for that pipe and where feasible use the longest flex 
possible/reasonably priced vs just adding a hung section.

Mike Morey
CFPS 3229 • NICET S.E.T. 123677
Project Manager • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive • Fort Wayne, IN • 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]
[cid:[email protected]]

From: [email protected] <[email protected]>
Sent: Thursday, May 11, 2023 12:41 PM
To: [email protected]
Subject: [Sprinklerforum] Flex Drops in excess of 100psi

Having an internal discussion, and the thought came up. . , Are there any 
discussions or considerations on the reduced arm over length when pressure is 
above 100psi? In other words, since the common flex fittings are rated to 
175psi in a bracket,
ZjQcmQRYFpfptBannerStart
Be Careful With This Message
The sender's identity could not be verified and someone may be impersonating 
the sender.
ZjQcmQRYFpfptBannerEnd
Having an internal discussion, and the thought came up..,

Are there any discussions or considerations on the reduced arm over length when 
pressure is above 100psi?

In other words, since the common flex fittings are rated to 175psi in a 
bracket, attached to a ceiling assembly, can we go to 36” for 1” with more than 
100psi at the sprinkler?

I know as written you cannot. But was wondering if this had been brought up.

R/
Matt

This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to