Travis raises the ultimate good point regarding self-storage: MANY small businesses use these facilities to store more hazardous stuff than the household goods most of us think of when considering self-storage. Let’s use a small discount furniture store as a beta: they may store upholstered backstock in a mini-storage cell, including mattresses and box springs.
So we have Expanded Group A more than 5’, but… does that define the entire facility? Methinks not, so what we do (and we actually work on a lot of these in the Southwest) is propose a double density to the fire official. The premise is OH2 is adequate as a basis of design overall (and I believe that it is) but we also include a second design area composed of the most hydraulically demanding 3 contiguous cells at .40 density. If a cell loaded with plastics lights up, the system will have the capacity to deliver a high density on both sides of it as well as over the involved fuel. Self-storage sprinkler layouts often create OH design areas with 35 sprinklers in them, so proving the .40 across four cells generally has no effect on the overall system sizing. It’s more of a comfort enhancement drug… My opinion only, Steve L. From: Travis Mack <[email protected]> Sent: Friday, January 20, 2023 7:35 AM To: Discussion list on issues relating to automatic fire sprinklers <[email protected]> Subject: [Sprinklerforum] Re: Self Storage In my opinion, these are often protected by systems for OH2. However, I believe they should be EH2 at a minimum. There are too many unknowns of what will be in the storage units. Travis Mack, SET M.E.P.CAD | 181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074 www.mepcad.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.mepcad.com%2f&c=E,1,VnUdVENxHi5EfReXNlDlMm53-i0iQ4aDqDmBEIrsdvcjraAvysTkEA3cdancd5C-YuLOO1Kazh8mbILb0XRi2ySj-bsvuYzh5A2J3gyhxnVz40eaVmnL6SFb59k,&typo=1> | m: 480.547.9348 AutoSPRINK | AutoSPRINK FAB | AutoSPRINK RVT | AlarmCAD From: Shawn Foor <[email protected]<mailto:[email protected]>> Sent: Friday, January 20, 2023 7:46 AM To: Discussion list on issues relating to automatic fire sprinklers <[email protected]<mailto:[email protected]>> Subject: [Sprinklerforum] Re: Self Storage I would say minimum OHII can also see EHII. I am assuming would have to remain dry so you have to increase to 1950 and depending on slope of roof maybe even 2535 sqft On Fri, Jan 20, 2023 at 8:39 AM Fpdcdesign <[email protected]<mailto:[email protected]>> wrote: What is the latest thought on the demand for a self storage location? I am working on an existing location with 8ft high “rooms” with no ceiling (not a Pod type). The existing system consists of two 1920s or 30s dry pipe, pipe schedule system. 6” DPVs. I do not know if any hydraulic calculations have been done previously. The plan is to add a backflow preventer and an FDC, but I will need to do some analysis for the addition of the backflow. I’m trying to avoid as much of a horror show as possible. Normally I would say that this would be a great job for my competition but I can’t get out of it. Also, each dry valve has a 6” bypass around it with a normally closed OS&Y. Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080<tel:860-535-2080> (ofc) 860-554-7054<tel:860-554-7054> (fax) 860-608-4559<tel:860-608-4559> (cell) _________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2flists.firesprinkler.org%2flist%2fsprinklerforum.lists.firesprinkler.org&c=E,1,lCcbbx_DZuV8Q5TeggvVbeHHG7cDSBV5JWYHLZnvFT9spZi3ypYXK_TNb12NXwXzxnnCzgcanzDfNE7qMhfhZ6Pbj_6Sin6Y2mWeczQBGsHWZZ7RID1A&typo=1> To unsubscribe send an email to [email protected]<mailto:[email protected]> -- Shawn Foor, SET FOOR DESIGN, LLC 10208 E 98TH ST TULSA, OK 74133 P:918-237-1400
_________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to [email protected]