I would say minimum OHII can also see EHII. I am assuming would have to remain dry so you have to increase to 1950 and depending on slope of roof maybe even 2535 sqft
On Fri, Jan 20, 2023 at 8:39 AM Fpdcdesign <[email protected]> wrote: > What is the latest thought on the demand for a self storage location? I am > working on an existing location with 8ft high “rooms” with no ceiling (not > a Pod type). > > The existing system consists of two 1920s or 30s dry pipe, pipe schedule > system. 6” DPVs. I do not know if any hydraulic calculations have been done > previously. The plan is to add a backflow preventer and an FDC, but I will > need to do some analysis for the addition of the backflow. I’m trying to > avoid as much of a horror show as possible. Normally I would say that this > would be a great job for my competition but I can’t get out of it. > > Also, each dry valve has a 6” bypass around it with a normally closed > OS&Y. > > > > Todd G Williams, PE > Fire Protection Design/Consulting > Stonington, CT > 860-535-2080 (ofc) > 860-554-7054 (fax) > 860-608-4559 (cell) > > _________________________________________________________ > SprinklerForum mailing list: > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org > To unsubscribe send an email to > [email protected] -- Shawn Foor, SET *FOOR DESIGN, LLC* *10208 E 98TH ST* *TULSA, OK 74133* *P:918-237-1400*