Could you just put a single head below the diffuser, on the side close to the 
return grill, and let that head serve as protection under both obstructions? Or 
drop a single head with a water shield right between the two?

It looks like the actual area would be small enough to be covered by one 
sprinkler.

-Kyle M

From: Luis Perea <[email protected]>
Sent: Wednesday, October 5, 2022 2:19 PM
To: 'Discussion list on issues relating to automatic fire sprinklers' 
<[email protected]>
Subject: [EXTERNAL] [Sprinklerforum] ESFR Sprinkler Under Obstruction

Hi everyone,

Per NFPA-13 i can“t find if it's mandatory to install a sprinkler under the 
HVAC extraction Grill, the size of the duct it is clearly an obstruction and 
the option i have been thinking is to install the sprinkler with a baffle under 
the grill.
Does anyone know if this is correct or have any other solution?

[cid:[email protected]]

Thank you.