I have come across an existing building with multiple riser and a new addition the new addition design criteria is 12 16.8 ESFR sprinkler with a minimum of 52 PSI. The existing water supply is not sufficient to supply this. Is there any code that does not allow the suction side of a fire pump to be connected to the bottom of an existing riser so that the fire pump only supply's the water in the new addition?
Bobby Welch | Sprinkler Systems Designer KOORSEN FIRE & SECURITY 3577 Concorde Rd, Vandalia, OH 45377 P 937.641.8403 | Ext. 0318 | M 937.594.8457 bobby.we...@koorsen.com<mailto:bobby.we...@koorsen.com> | www.koorsen.com<http://www.koorsen.com> 24x7x365 Service: 937.660.7050 | servic...@koorsen.com
_________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org