Fast response elements do not universally equate to quick response
sprinklers.

https://www.vikinggroupinc.com/sites/default/files/documents/Automatic%20Sprinkler%20Thermal%20Sensitivity.pdf

On Tue, Sep 27, 2022 at 10:58 AM Matthew J Willis <[email protected]>
wrote:

> Todd,
>
>
>
> What are you protecting?
>
>
>
> The wording for extending one hazard into another is a sufficient heat
> barrier.
>
>
>
> You may be chasing rabbits.
>
>
>
> R/
>
> Matt
>
>
>
>
>
> *Matthew J. Willis, CWBSP*
>
> Design Manager
>
>
>
> *Rapid Fire Protection, Inc.*
>
> 600 E. Carlson St. Suite AB | Cheyenne, WY. 82009
>
> Office (307) 426-4077 ext. 404
>
> Direct (307) 316-6630
>
> Cell (605) 391-2733
>
>
>
>
>
> *From:* Fpdcdesign <[email protected]>
> *Sent:* Tuesday, September 27, 2022 11:04 AM
> *To:* Discussion list on issues relating to automatic fire sprinklers <
> [email protected]>
> *Subject:* [Sprinklerforum] Re: Adding sprinklers to system with mixed
> SR/QR listing
>
>
>
> Compartment does not apply here.
>
>
>
> The conclusion I and coming to is that we need to closely match the RTI of
> the new sprinklers to the RTI of the EC sprinkler, regardless of how the
> latter is listed.
>
>
>
>
>
>
> On Sep 27, 2022 at 8:15 AM, <Sean Conlin
> <[email protected]>> wrote:
>
> If the EC sprinkler used is listed as QR in its current application, then
> the new area of work has to use QR unless the area of work is located in a
> separate compartment.   Check the definition of compartment to see if the
> soffit you mention can work for you.
>
>
>
> Regards,
>
>
>
> Sean W Conlin
>
> Demand Sprinkler Design Inc.
>
> 37 Summerfield Crescent
>
> Brampton, ON L6X 4K4
>
> P: 905 216-0922
>
>
>
>
>
> On Sep 26, 2022, at 12:42 PM, Fpdcdesign <[email protected]> wrote:
>
> 
>
> I am working on to an addition to an existing system that has Tyco EC-11
> pendent sprinklers. According to the data sheet, these sprinklers may be QR
> in some circumstances and SR in others. The addition I am working on will
> be using standard coverage sprinklers. The space is open to the area with
> the EC-11 sprinklers but separated by a deep soffit. The design of the
> EC-11 is such that they are considered standard response by the listing.
> The obvious question is QR or SR for the new sprinklers? I am assuming QR
> because that is closer to the response time of the EC-11s despite the SR
> listing, but I am being questioned on this. Thoughts?
>
>
>
> Todd G Williams, PE
>
> Fire Protection Design/Consulting
>
> Stonington, CT
>
> 860-535-2080 (ofc)
>
> 860-554-7054  (fax)
>
> 860-608-4559 (cell)
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>
> _________________________________________________________ SprinklerForum
> mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to