Compartment does not apply here.   
  

  
The conclusion I and coming to is that we need to closely match the RTI of the 
new sprinklers to the RTI of the EC sprinkler, regardless of how the latter is 
listed.   
  
  
  
  
  
  
  

  
  
>   
> On Sep 27, 2022 at 8:15 AM,  <Sean Conlin 
> (mailto:[email protected])>  wrote:
>   
>   
>   If the EC sprinkler used is listed as QR in its current application, then 
> the new area of work has to use QR unless the area of work is located in a 
> separate compartment.     Check the definition of compartment to see if the 
> soffit you mention can work for you.     
>
>   
> Regards,  
>
>   
> Sean W Conlin
>   
> Demand Sprinkler Design Inc.   
>   
> 37 Summerfield Crescent   
>   
> Brampton, ON L6X 4K4
>   
>   
> P: 905 216-0922
>   
>
>     
>
>   
> > On Sep 26, 2022, at 12:42 PM, Fpdcdesign  <[email protected]>  wrote:
> >   
>     
> >   
> >   
> >   
> >
> >   I am working on to an addition to an existing system that has Tyco EC-11 
> > pendent sprinklers. According to the data sheet, these sprinklers may be QR 
> > in some circumstances and SR in others. The addition I am working on will 
> > be using standard coverage sprinklers. The space is open to the area with 
> > the EC-11 sprinklers but separated by a deep soffit. The design of the 
> > EC-11 is such that they are considered standard response by the listing. 
> > The obvious question is QR or SR for the new sprinklers? I am assuming QR 
> > because that is closer to the response time of the EC-11s despite the SR 
> > listing, but I am being questioned on this. Thoughts?
> >   
> >   
> >   
> >  Todd G Williams, PE  
> > Fire Protection Design/Consulting
> >   
> > Stonington, CT
> >   
> > 860-535-2080 (tel:860-535-2080)  (ofc)
> >   
> > 860-554-7054 (tel:860-554-7054)     (fax)
> >   
> > 860-608-4559 (tel:860-608-4559)  (cell)
> >   
> >   
> >   
> >   
> >
> >   
> >   
> >   _________________________________________________________
> >   SprinklerForum mailing list:
> >   
> > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> >   To unsubscribe send an email to 
> > [email protected]      
> > _________________________________________________________ SprinklerForum 
> > mailing list: 
> > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> > To unsubscribe send an email to 
> > [email protected]            
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to