NFPA #13 (2013) section 8.12.5.3 Continuous Obstructions Below Sprinkler.

Building is 40'-0" high and is protected with ESFR K25 sprinkler heads.

We have an electrical cable tray that is 1'-0" wide and they have located it 
below a line of ESFR sprinkler heads. The cable tray is located 25'-0" below 
the sprinkler heads.

Code does not give a distance below but only states that it needs to be locate 
1'-0" to the side of the sprinkler heads or you need to provide sprinkler 
protection below, but my logical brain says this should not be a problem.

Comments.

Thank You

James Crawford
Phaser Fire Protection Ltd.
Phone 604-888-0318
Cel: 604-790-0938
Email [email protected]<mailto:[email protected]>
Web: www.phaserfire.ca<http://www.phaserfire.ca>