NFPA #13 (2013) section 8.12.5.3 Continuous Obstructions Below Sprinkler. Building is 40'-0" high and is protected with ESFR K25 sprinkler heads.
We have an electrical cable tray that is 1'-0" wide and they have located it below a line of ESFR sprinkler heads. The cable tray is located 25'-0" below the sprinkler heads. Code does not give a distance below but only states that it needs to be locate 1'-0" to the side of the sprinkler heads or you need to provide sprinkler protection below, but my logical brain says this should not be a problem. Comments. Thank You James Crawford Phaser Fire Protection Ltd. Phone 604-888-0318 Cel: 604-790-0938 Email [email protected]<mailto:[email protected]> Web: www.phaserfire.ca<http://www.phaserfire.ca>