Great pump.  Concrete and grout both weigh 100#/cuft

 

From: Anthony Carrizosa <[email protected]> 
Sent: Thursday, September 15, 2022 10:42 AM
To: Discussion list on issues relating to automatic fire sprinklers
<[email protected]>
Subject: [Sprinklerforum] Re: Fire pump package weight ?

 

Here is the motor and pump with the weights shown.

 

 

From: Tom Duross <[email protected]> 
Sent: Thursday, September 15, 2022 7:23 AM
To: 'Discussion list on issues relating to automatic fire sprinklers'
<[email protected]>
Subject: [Sprinklerforum] Re: Fire pump package weight ?

 

If your sizing the mass/weight of the concrete base and grout (1 ½”
minimum), for a low speed it should be equal or greater the pump/base and
motor weight.  I think 2600# is everything.

 

From: Anthony Carrizosa <[email protected]
<mailto:[email protected]> > 
Sent: Thursday, September 15, 2022 10:14 AM
To: Discussion list on issues relating to automatic fire sprinklers
<[email protected]
<mailto:[email protected]> >
Subject: [Sprinklerforum] Re: Fire pump package weight ?

 



 

-----Original Message-----
From: Sean Lockyer <[email protected]
<mailto:[email protected]> > 
Sent: Wednesday, September 14, 2022 9:25 PM
To: Discussion list on issues relating to automatic fire sprinklers
<[email protected]
<mailto:[email protected]> >
Subject: [Sprinklerforum] Re: Fire pump package weight ?

 

1500 gpm, 100 hp

 

-----Original Message-----

From: Art Tiroly < <mailto:[email protected]> [email protected]>


Sent: Thursday, September 15, 2022 12:22 AM

To: 'Discussion list on issues relating to automatic fire sprinklers' <
<mailto:[email protected]>
[email protected]>

Subject: [Sprinklerforum] Re: Fire pump package weight ?

 

What GPM and what HP?

 

-----Original Message-----

From: Sean Lockyer < <mailto:[email protected]>
[email protected]>

Sent: Thursday, September 15, 2022 12:00 AM

To:  <mailto:[email protected]>
[email protected]

Subject: [Sprinklerforum] Fire pump package weight ?

 

About how much would you surmise the weight of an electric horizontal
split-case fire pump package (include enclosure) would weigh ? 

 

            Sean Lockyer

            Project Designer                                   

  

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

_________________________________________________________

SprinklerForum mailing list:

 
<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2flists.firesprinkler.org
%2flist%2fsprinklerforum.lists.firesprinkler.org&c=E,1,DfzSzTeqWUwarN-Dg292_
JHPnkxXliCwra_zUsxEPeNK7PR3iZdBgjK9KpCvs0jmeZ5EEd8DFYfFnlSMKZzfmFcRVZSmcjCMd
ZaeET79sZln1zk,&typo=1>
https://linkprotect.cudasvc.com/url?a=https%3a%2f%2flists.firesprinkler.org%
2flist%2fsprinklerforum.lists.firesprinkler.org&c=E,1,DfzSzTeqWUwarN-Dg292_J
HPnkxXliCwra_zUsxEPeNK7PR3iZdBgjK9KpCvs0jmeZ5EEd8DFYfFnlSMKZzfmFcRVZSmcjCMdZ
aeET79sZln1zk,&typo=1

To unsubscribe send an email to
<mailto:[email protected]>
[email protected]

 

_________________________________________________________

SprinklerForum mailing list:

 
<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2flists.firesprinkler.org
%2flist%2fsprinklerforum.lists.firesprinkler.org&c=E,1,ZfpulvtYBrq7UUlNxAntG
6zWFBbxg8fK3o-xYI0_BrOznQ1p8IUp0pXvt2Ab3RsaMBqGDcO9v2VMFtzsflM871HRujsyETSkC
HERHQsMiWLuf0wDkDAi5F0YAYg,&typo=1>
https://linkprotect.cudasvc.com/url?a=https%3a%2f%2flists.firesprinkler.org%
2flist%2fsprinklerforum.lists.firesprinkler.org&c=E,1,ZfpulvtYBrq7UUlNxAntG6
zWFBbxg8fK3o-xYI0_BrOznQ1p8IUp0pXvt2Ab3RsaMBqGDcO9v2VMFtzsflM871HRujsyETSkCH
ERHQsMiWLuf0wDkDAi5F0YAYg,&typo=1

To unsubscribe send an email to
<mailto:[email protected]>
[email protected]

 

_________________________________________________________

SprinklerForum mailing list:

 
<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2flists.firesprinkler.org
%2flist%2fsprinklerforum.lists.firesprinkler.org&c=E,1,WGITz_JTvVaQUlgoj9Tsl
dhaGiPP2O3Kx3o4SgafVikVHSfW-JCPv9FaN6yMYono2cAGTVb3LtQ0YNWDXoNIsXIu5cHladNUd
rAJCMsxD35KUBWvWx0B&typo=1>
https://linkprotect.cudasvc.com/url?a=https%3a%2f%2flists.firesprinkler.org%
2flist%2fsprinklerforum.lists.firesprinkler.org&c=E,1,WGITz_JTvVaQUlgoj9Tsld
haGiPP2O3Kx3o4SgafVikVHSfW-JCPv9FaN6yMYono2cAGTVb3LtQ0YNWDXoNIsXIu5cHladNUdr
AJCMsxD35KUBWvWx0B&typo=1

To unsubscribe send an email to
<mailto:[email protected]>
[email protected]

 

Anthony Carrizosa | Fire Protection Estimator / Project Manager

7855 S 206th St Kent, WA 98032

Cell: 206-679-5283 | Direct: 253-341-4593 | Office: 253-872-7222

 



https://archerconstruction.com
<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2farcherconstruction.com%
2f&c=E,1,TbX_24i9fiZbrv7cVekoPOZkiwsLtwzrjR83-4jEOlXlphnc0GP59tTb1MxZMbLyZzV
x7BFB1Y-nN5Dlu8K1jNjM8m6BpylpBdpUr-O7GVif&typo=1> 

 

 

 

 

 

Anthony Carrizosa | Fire Protection Estimator / Project Manager

7855 S 206th St Kent, WA 98032

Cell: 206-679-5283 | Direct: 253-341-4593 | Office: 253-872-7222

 



https://archerconstruction.com <https://archerconstruction.com/> 

 

 

 

 

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to