What of the pump house/enclosure though ?

From: Tom Duross <[email protected]>
Sent: Thursday, September 15, 2022 10:23 AM
To: 'Discussion list on issues relating to automatic fire sprinklers' 
<[email protected]>
Subject: [Sprinklerforum] Re: Fire pump package weight ?

If your sizing the mass/weight of the concrete base and grout (1 ½" minimum), 
for a low speed it should be equal or greater the pump/base and motor weight.  
I think 2600# is everything.

From: Anthony Carrizosa <[email protected]>
Sent: Thursday, September 15, 2022 10:14 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Fire pump package weight ?


[cid:[email protected]]



-----Original Message-----
From: Sean Lockyer <[email protected]>
Sent: Wednesday, September 14, 2022 9:25 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Fire pump package weight ?



1500 gpm, 100 hp



-----Original Message-----

From: Art Tiroly <[email protected]<mailto:[email protected]>>

Sent: Thursday, September 15, 2022 12:22 AM

To: 'Discussion list on issues relating to automatic fire sprinklers' 
<[email protected]<mailto:[email protected]>>

Subject: [Sprinklerforum] Re: Fire pump package weight ?



What GPM and what HP?



-----Original Message-----

From: Sean Lockyer 
<[email protected]<mailto:[email protected]>>

Sent: Thursday, September 15, 2022 12:00 AM

To: 
[email protected]<mailto:[email protected]>

Subject: [Sprinklerforum] Fire pump package weight ?



About how much would you surmise the weight of an electric horizontal 
split-case fire pump package (include enclosure) would weigh ?



            Sean Lockyer

            Project Designer

































_________________________________________________________

SprinklerForum mailing list:

https://linkprotect.cudasvc.com/url?a=https%3a%2f%2flists.firesprinkler.org%2flist%2fsprinklerforum.lists.firesprinkler.org&c=E,1,DfzSzTeqWUwarN-Dg292_JHPnkxXliCwra_zUsxEPeNK7PR3iZdBgjK9KpCvs0jmeZ5EEd8DFYfFnlSMKZzfmFcRVZSmcjCMdZaeET79sZln1zk,&typo=1

To unsubscribe send an email to 
[email protected]<mailto:[email protected]>



_________________________________________________________

SprinklerForum mailing list:

https://linkprotect.cudasvc.com/url?a=https%3a%2f%2flists.firesprinkler.org%2flist%2fsprinklerforum.lists.firesprinkler.org&c=E,1,ZfpulvtYBrq7UUlNxAntG6zWFBbxg8fK3o-xYI0_BrOznQ1p8IUp0pXvt2Ab3RsaMBqGDcO9v2VMFtzsflM871HRujsyETSkCHERHQsMiWLuf0wDkDAi5F0YAYg,&typo=1

To unsubscribe send an email to 
[email protected]<mailto:[email protected]>



_________________________________________________________

SprinklerForum mailing list:

https://linkprotect.cudasvc.com/url?a=https%3a%2f%2flists.firesprinkler.org%2flist%2fsprinklerforum.lists.firesprinkler.org&c=E,1,WGITz_JTvVaQUlgoj9TsldhaGiPP2O3Kx3o4SgafVikVHSfW-JCPv9FaN6yMYono2cAGTVb3LtQ0YNWDXoNIsXIu5cHladNUdrAJCMsxD35KUBWvWx0B&typo=1

To unsubscribe send an email to 
[email protected]<mailto:[email protected]>

Anthony Carrizosa | Fire Protection Estimator / Project Manager
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Direct: 253-341-4593 | Office: 253-872-7222

[Image removed by sender.]
https://archerconstruction.com<https://archerconstruction.com/>




_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to