But this also underscores that water districts are staffed by and their systems 
improved and maintained by human beings, so whether it’s a public or private 
fire main system, ITM flow testing is a critical aspect of “reliability” as we 
assume our water supplies to be, especially when connected to a public system.  
 Models for design, forward flow testing for maintenance – we need both.

6-7 years ago we were designing sprinkler and site fire systems for a large 
community college complex.  The water district is well know to run very high 
pressures and (usually) high flow rates in their systems, including the zone 
feeding the subject campus.  There are three laterals from the public to the 
private looped system, each one 8” in diameter.   We had 120 static on site 
with about 80 residual if I recall correctly, but couldn’t get more than 1,100 
GPM out of a 2½” port adjacent to the site.  Large complex, Type 2, local FD 
only allowing 25% reduction for sprinklers, so needed 3,250 or something like 
that and it extrapolated out to only about 10 PSI residual at that flow.   
Water district’s model showed that the mains feeding the campus were easily 
capable of meeting demand, but we couldn’t get it out of the hydrant on site.   
I pitched the school that they pay us a wee bit extra to exercise all their 
hydrants and valves, so we did that on a Saturday.   We found 7 (SEVEN!) 
partially closed and one completely closed valve on their system and once 
everything opened up we easily got 3,300 out of a 4” with about 45 psi residual.

For those who aren’t familiar with models, don’t be scared.  But we mustn’t 
turn away from flow testing and ITM and we have to hope that public water 
purveyors are exercising their systems too.

Steve L.

From: Greg McGahan <[email protected]>
Sent: Tuesday, September 06, 2022 7:10 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: [EXTERNAL] Hydrant flow tests

How many flow tests have you seen that underperformed due to a closed valve, 
broken valve (appeared to be open), disconnected piping that was never 
reconnected etc?
Personally? Too many to not be concerned about solely relying on models.
My two cents worth (adjusted for inflation).



On Tue, Sep 6, 2022 at 8:46 AM cw bamford 
<[email protected]<mailto:[email protected]>> wrote:
Computer Programs  --  DATA --  garbage in = garbage output

Locally Most information is Good with the computer models having a 10%  or  10 
psi safety factor.

I have received Information that has been has been BOTH  high psi Static  and  
LOW   psi  static  &  GPM at 20 psi  that goes off the HASS HRSS chart (over 
9999 gpm)

I have helped Local AHJ and Water Dist.  to confirm DATA
 and   asked to put Gauge on Hydrant to check static psi.
 flushed a Local private hydrants  and Collected Data to compare to Water Info
flushed UNDERGROUND  and Collect DATA

A few local Water Districts oversee Hydrant Flow Tests  (Are they being flushed 
every 5 years?)

and a Few jobsites  may have 88 psi Static  ....  but  10% off  another 5% for 
worst case in 25 years   and they give us 72 psi static
well with a few
74' building with Attic Dry    or   a
50 year old Warehouse  with storage
I NEED ACTUAL  STATIC   PSI   FOR  possible fire pump  design
NOT flow test from a computer model that says 66 psi  and  flowing  3000 gpm at 
50 psi  and  limits water to 10 fps (how many hydants are flowing?)

(Does City of R....& L....  Fire think about velocity ? when we do actual of 
standpipe flow tests NO )  around
200 psi @ Pumper Truck  +- 175 psi at FDC  165 @ Riser flowing 1100 - 750 gpm 
with 100 psi residual at High Point

RECOMMENDATIONS  when Water Districts flush hydrants Collect Data for Computer 
Models.

Chuck Bamford S.E.T.





On Wed, Aug 31, 2022 at 11:22 AM Fpdcdesign 
<[email protected]<mailto:[email protected]>> wrote:
I think a lot of this depends on the sophistication of the software and 
hardware used, which could also be a function of the size of the water company. 
In the Northeast, we have a lot of small water companies that only service a 
specific town or section of town. Near the larger cities, you get regional 
authorities that cover several towns but there may or not be any 
interconnections. Also, several municipal water companies have been bought up 
by holding companies but they still operate as independent units. They don’t 
have the resources to spend on a sophisticated modeling system.

One of the companies that services the town I live in tried a modeling system. 
It consisted of little more than a 3D computer model of the system connected to 
a pump. Something I could do with Autosprink. I believe they had a run of 
unlined cast iron pipe from 1888 listed as C=120 (or the D-W equivalent). 
Needless to say the accuracy is a joke. I think it has been abandoned.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080<tel:860-535-2080> (ofc)
860-554-7054<tel:860-554-7054>  (fax)
860-608-4559<tel:860-608-4559> (cell)



On Aug 31, 2022 at 1:15 PM, <Steve Leyton<mailto:[email protected]>> 
wrote:
T-Mack’s comments reminded me of one other distinct advantage to models – I can 
get two or more per project relatively easily if I need to.   Our firm designs 
a lot of private hydrant systems in addition to building sprinkler systems, so 
the benchmark we need for highest accuracy might be 3,000 GPM flow or 350 gpm 
flow.  As others have noted, the higher the flow rate the more accurate the 
data (vs. extrapolation), and with most agencies, I can request models at 
whatever fire flow rate I choose.

Steve

From: [email protected]<mailto:[email protected]> 
<[email protected]<mailto:[email protected]>>
Sent: Wednesday, August 31, 2022 9:46 AM
To: 
[email protected]<mailto:[email protected]>
Subject: [Sprinklerforum] Re: [EXTERNAL] Hydrant flow tests

Maybe because I am in the SW with Steve, I agree 100% with his statements here. 
 We can get situations modeled for basically anything we want regarding the 
water supply.  As Steve mentioned, many water agencies have decades of data to 
accurately model this stuff.  I have to ask why we will rely on hydraulic 
calculation models for our fire sprinkler systems, if we won’t rely on similar 
calculation models for the water supply?  The math doesn’t change just because 
it is a sprinkler vs a hydrant.

Our experience has been more positive with models than with actual flow 
testing.  We’ve had customers go “flow test shopping” where I found out later 
that they did multiple flow tests and gave us the best one that they obtained.  
Well, that’s great if you can guarantee a fire will only occur during that time 
frame.  The computer models will account for peak demand, anticipated changes, 
and other things that a simple flow test can not account for.

While I am old school and do like to have it confirmed by an actual flow test 
if possible, I tend to feel the models are more reliable and accurate over 
longer periods.  Now, all of this is to say that it is based on the model 
database of information to be accurate.  If there are errors in the database or 
user entering the information for the model it fails.  That is no different 
than someone using an un-calibrated gauge, not applying pumper coefficients or 
getting incorrect hydrant coefficients, let alone not choosing the worst-case 
time of day for a flow test.

Please rate our customer 
service<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fsurvey.medallia.com%2f%3femailsignature%26fc%3d3539%26bg%3dFire%2520and%2520Fabrication&c=E,1,wv1KVigAKuTRqcaSNc4pOZWCeagx-cP1kMlCKE8h7pS48OQSn6sq5itvRRdcmq8opQ2Q6Jx5GIdlWoWFi--9DawdWzMxzMf3H9pfJ-7GSaKFDeY,&typo=1>

Travis Mack, RME-G, COC, SET
Senior Engineering Manager
MFP Design
480-505-9271 ext. 700 C: 480-272-2471
[email protected]<mailto:[email protected]>
[email protected]<mailto:[email protected]>
www.mfpdesign.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.mfpdesign.com&c=E,1,i9qf3bbsyv8viIjgOz35g6OUEOU8y_Fb35HidPh5Fy5fUjakm34El4fK3J0RuCX-nr30TdcTmyQhK0NBpYGnIn02l4eaRI9g28fnhDYTPSDjBA,,&typo=1>

Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>

From: Steve Leyton 
<[email protected]<mailto:[email protected]>>
Sent: Wednesday, August 31, 2022 9:35 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: [EXTERNAL] Hydrant flow tests

I respectfully, but stridently disagree.   To this comment and Rick’s 
overarching question, I would offer that our experience over the past 10+ years 
has been that these models are not only accurate, they are highly so and can be 
programmed for eventualities and conditions that flow tests simply cannot 
reflect, because they are a measurement of the “right now” only.  But I would 
offer an bold asterisk on my comments because they are based on regionality and 
I’m in the SWUSA, where water management has been a critical thing for a full 
generation now.

Because of drought concerns going back 20+ years, many water agencies stopped 
doing flow tests and began to meter their systems.  Today, nearly all water 
agencies in California will only grant a permit to do a physical flow test if 
there are compelling circumstances, and we rely on models.   Using San Diego 
County as an example, water districts began installing sensors 25 years ago and 
have been collect metadata on overall system performance for dozens of years; 
these systems are in fact predictable if the database used to calculate 
performance is well-populated and highly detailed.   I was going to offer Rick 
the anecdote of how we designed a whole campus high school 15 years ago, in a 
subdivision that was brand new.  The only “flow data” we had to work with was 
the master developer’s civil engineering water study, which was based on the 
zone model from the water district.   And it said that the static was going to 
be so high (182) that we needed to install pressure reducing valves on the 
supply side of the backflows feeding the site loop.   We also used the model 
for sprinkler hydraulics, but corrected the pressures downward for the PRV 
settings.   When the permanent system was commissioned into service (two years 
later and with sprinkler systems 80-90% installed) the static pressure was 181 
and the residual was exactly the same as modeled.

Programmability of models enables simulation of worst-case scenarios, 
particularly peak day demand, annual drought predictions and legacy drought 
conditions.   This is extremely important in the West as our water levels are 
literally dropping every year, so maybe that’s why our water agencies have 
established such high standards of care for modeling.   City of San Diego 
doesn’t require that you take 10% off of their models any longer – why?  
Because they program peak day demand, legacy drought levels and an additional 
safety factor.   When they first started this practice, the FP community was 
going nuts – field conditions showed 10-20 PSI more pressure at the hydrants in 
some cases.  Yes, pipe sizing was affected,  but if we’re talking about safety 
and prudence (without consideration for the cost-impact, obviously), this 
methodology yields solidly conservative data for basis of design.

Chains are only as strong as their weakest link and physical flow testing only 
reflects current conditions.  Was the test done during a peak day demand 
window?  Was the test measured with a $10-15 spring loaded gauge (up to 8-10% 
error) or a calibrated liquid-filled one with a 1% error or less?   Was the 
test even taken by skilled personnel?    My opinion on this has swung – I’m now 
pro-model and we look at physical testing as an archaic practice, and I’m a 
shamelessly analogue Boomer.


Yours in the name of fire safety and progress,
Steve L.



From: Prahl, Craig <[email protected]<mailto:[email protected]>>
Sent: Wednesday, August 31, 2022 8:10 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: [EXTERNAL] Hydrant flow tests

Having experienced bogus results from computer modeling on more than one 
occasion, nothing matches the actual flow of the hydrant systems.

Most recently I got a water report from a local municipality who generated the 
info via their water modeling software.  It said I could expect 6700 gpm from 
the system……. via 8” lines at 10 fps!   Nope, don’t think that’s going to be a 
real thing.

Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 
[email protected]<mailto:[email protected]> | 
www.jacobs.com<http://www.jacobs.com/>
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS



From: Rick Matsuda <[email protected]<mailto:[email protected]>>
Sent: Wednesday, August 31, 2022 9:51 AM
To: 
[email protected]<mailto:[email protected]>
Subject: [EXTERNAL] [Sprinklerforum] Hydrant flow tests

I know that an accurate flow test is critical for the sprinkler system 
design, but I’ve heard several discussions recently about water conservation 
during our drought conditions across the SW states.

With all our technology, is it possible to develop an accurate computer 
modeling program for water departments to use in lieu of flow tests? Even with 
the program, I think there would still be a need for some flow tests to verify 
the program results, but maybe not as many as now.

I’m not taking any pro/con position regarding this issue. I’m just providing 
food for thought for the future as our need for water increases and our 
resources diminish. Adequate water is the key for our industry.

It’s ironic cause we get more wild fires due to the drought, and then we have 
to use more water to fight the fires.
Rick Matsuda


________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_________________________________________________________ SprinklerForum 
mailing list: 
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2flists.firesprinkler.org%2flist%2fsprinklerforum.lists.firesprinkler.org&c=E,1,iLlDUrEOl_r1V4_kXJITzTjUmzrwlyrvpIor_at_UsbSOoVa6xM91gLLV_WRk2PsxwDpGtNSu0_bMAvWsrvSU1fx71wP_eAZioaR-TzH-dnJwJRtB9S6QtWa&typo=1>
 To unsubscribe send an email to 
[email protected]<mailto:[email protected]>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2flists.firesprinkler.org%2flist%2fsprinklerforum.lists.firesprinkler.org&c=E,1,NxYDZiIHkfCclIb_lH7HwWn8UzRPb2HLn2MWwl4_AnrpDcNPsFoiw4uAhJY4gziuDxTXrGhQIc2y8pwOc0L_H7KLooG2yaA-wRbDdvFBQFe7hZTwfbCn4VBSAFw,&typo=1>
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2flists.firesprinkler.org%2flist%2fsprinklerforum.lists.firesprinkler.org&c=E,1,S-jRgwxw-YOZx5KraE1BSX_Ddr_15xn32yozHg-hG9QLHmOyO65ESMqidcnlsBEGELVayqmSO2GO6coMEbNtfAxRtz5k1XbrrAiI8-wV5AiYdGDxwQCvpw,,&typo=1>
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>


--
Greg McGahan
Genesis Fire Services, LLC
4912 Glover Lane. Milton, FL 32570
P- 850-637-8535
C- 850-712-9555
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to