Before the largest of our water purveyors went with models about twenty points 
were selected at which the fire marshal’s office conducted flow tests in the 
field. Maybe one per 2 sq miles (?) to give some idea of scope. Not distributed 
evenly of course. This check on model’s accuracy was probably invisible to the 
sprinkler designers. 

Best.

Bruce Verhei 

> On 08/31/2022 9:35 AM Steve Leyton <[email protected]> wrote:
> 
>  
> I respectfully, but stridently disagree.   To this comment and Rick’s 
> overarching question, I would offer that our experience over the past 10+ 
> years has been that these models are not only accurate, they are highly so 
> and can be programmed for eventualities and conditions that flow tests simply 
> cannot reflect, because they are a measurement of the “right now” only.  But 
> I would offer an bold asterisk on my comments because they are based on 
> regionality and I’m in the SWUSA, where water management has been a critical 
> thing for a full generation now.
> 
> Because of drought concerns going back 20+ years, many water agencies stopped 
> doing flow tests and began to meter their systems.  Today, nearly all water 
> agencies in California will only grant a permit to do a physical flow test if 
> there are compelling circumstances, and we rely on models.   Using San Diego 
> County as an example, water districts began installing sensors 25 years ago 
> and have been collect metadata on overall system performance for dozens of 
> years; these systems are in fact predictable if the database used to 
> calculate performance is well-populated and highly detailed.   I was going to 
> offer Rick the anecdote of how we designed a whole campus high school 15 
> years ago, in a subdivision that was brand new.  The only “flow data” we had 
> to work with was the master developer’s civil engineering water study, which 
> was based on the zone model from the water district.   And it said that the 
> static was going to be so high (182) that we needed to install pressure 
> reducing valves on the supply side of the backflows feeding the site loop.   
> We also used the model for sprinkler hydraulics, but corrected the pressures 
> downward for the PRV settings.   When the permanent system was commissioned 
> into service (two years later and with sprinkler systems 80-90% installed) 
> the static pressure was 181 and the residual was exactly the same as modeled.
> 
> Programmability of models enables simulation of worst-case scenarios, 
> particularly peak day demand, annual drought predictions and legacy drought 
> conditions.   This is extremely important in the West as our water levels are 
> literally dropping every year, so maybe that’s why our water agencies have 
> established such high standards of care for modeling.   City of San Diego 
> doesn’t require that you take 10% off of their models any longer – why?  
> Because they program peak day demand, legacy drought levels and an additional 
> safety factor.   When they first started this practice, the FP community was 
> going nuts – field conditions showed 10-20 PSI more pressure at the hydrants 
> in some cases.  Yes, pipe sizing was affected,  but if we’re talking about 
> safety and prudence (without consideration for the cost-impact, obviously), 
> this methodology yields solidly conservative data for basis of design.
> 
> Chains are only as strong as their weakest link and physical flow testing 
> only reflects current conditions.  Was the test done during a peak day demand 
> window?  Was the test measured with a $10-15 spring loaded gauge (up to 8-10% 
> error) or a calibrated liquid-filled one with a 1% error or less?   Was the 
> test even taken by skilled personnel?    My opinion on this has swung – I’m 
> now pro-model and we look at physical testing as an archaic practice, and I’m 
> a shamelessly analogue Boomer.
> 
> 
> Yours in the name of fire safety and progress,
> Steve L.
> 
> 
> 
> From: Prahl, Craig <[email protected]>
> Sent: Wednesday, August 31, 2022 8:10 AM
> To: Discussion list on issues relating to automatic fire sprinklers 
> <[email protected]>
> Subject: [Sprinklerforum] Re: [EXTERNAL] Hydrant flow tests
> 
> Having experienced bogus results from computer modeling on more than one 
> occasion, nothing matches the actual flow of the hydrant systems.
> 
> Most recently I got a water report from a local municipality who generated 
> the info via their water modeling software.  It said I could expect 6700 gpm 
> from the system……. via 8” lines at 10 fps!   Nope, don’t think that’s going 
> to be a real thing.
> 
> Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 
> [email protected]<mailto:[email protected]> | 
> www.jacobs.com<http://www.jacobs.com/>
> 1041 East Butler Road   Greenville, South Carolina  29606
> CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS
> 
> 
> 
> From: Rick Matsuda <[email protected]<mailto:[email protected]>>
> Sent: Wednesday, August 31, 2022 9:51 AM
> To: 
> [email protected]<mailto:[email protected]>
> Subject: [EXTERNAL] [Sprinklerforum] Hydrant flow tests
> 
> I know that an accurate flow test is critical for the sprinkler system 
> design, but I’ve heard several discussions recently about water conservation 
> during our drought conditions across the SW states.
> 
> With all our technology, is it possible to develop an accurate computer 
> modeling program for water departments to use in lieu of flow tests? Even 
> with the program, I think there would still be a need for some flow tests to 
> verify the program results, but maybe not as many as now.
> 
> I’m not taking any pro/con position regarding this issue. I’m just providing 
> food for thought for the future as our need for water increases and our 
> resources diminish. Adequate water is the key for our industry.
> 
> It’s ironic cause we get more wild fires due to the drought, and then we have 
> to use more water to fight the fires.
> Rick Matsuda
> 
> 
> ________________________________
> 
> NOTICE - This communication may contain confidential and privileged 
> information that is for the sole use of the intended recipient. Any viewing, 
> copying or distribution of, or reliance on this message by unintended 
> recipients is strictly prohibited. If you have received this message in 
> error, please notify us immediately by replying to the message and deleting 
> it from your computer.
> 
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to [email protected]

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to