Generally an Architect would be responsible for determining how an area is
rated, including whether a sprinkler system is required. I would go back to
the owner and tell him to have the architect review the intumescent paint
and determine if it creates an adequate fire resistance for the space to be
considered as "non-combustible". Then send the architect's report to the
AHJ.
In similar types of circumstances I have always gone back to the owner or
consultant team and always put my position to them as "I deal with
sprinkler systems not fire ratings" it's up to someone else to determine If
and where we are putting a sprinkler system in place.

Thanks

Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
[email protected]
780 490 7602 office ext 202
780 490 7605 fax
780 777 0568 cell
780 718 2676 24h
Visit us at www.proudline.ca

Proudline now offers ULc listed monitoring services, please contact
[email protected] for more information






On Thu, Sep 1, 2022 at 8:28 AM Fpdcdesign <[email protected]> wrote:

> And the local AHJ says he’ll approve it if I approve it. And I do not
> want to get involved.
>
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860-535-2080 (ofc)
> 860-554-7054  (fax)
> 860-608-4559 (cell)
>
>
> On Sep 1, 2022 at 10:23 AM, <Bob Caputo <[email protected]>>
> wrote:
>
> This is true for impregnated fire treatment however this also weakens the
> structural member. There are intumescent paint on the market that can be
> applied but must be approved first by the local AHJ.
>
> The problem with these applications can be a lack of uniformity in the
> thickness applied (as with any coating) but section 1.5 allows alternatives
> were approved by the local AHJ
>
> On Thu, Sep 1, 2022 at 9:08 AM Anthony Carrizosa <
> [email protected]> wrote:
>
>> According to NFPA 703 NFPA 703 Fire Retardant – Treated Wood.
>>
>>
>>
>> This cannot be a paint applied after construction, but must be during the
>> wood manufacturing process.
>>
>>
>>
>>
>>
>> *Anthony Carrizosa *
>>
>> Project Manager *| *Fire Protection
>>
>> 7855 S 206
>> <https://www.google.com/maps/search/7855+S+206?entry=gmail&source=g>th
>> St Kent, WA 98032
>>
>> Cell: *206-679-5283* | Office Dir: *253-341-4593*
>>
>> https://archerconstruction.com
>> <https://linkprotect.cudasvc.com/url?a=https%3a%2f%2farcherconstruction.com%2f&c=E,1,Wdb65AWzMgSBzW3HDw91SfcRQCtxDUQKoJf-UowQ-WnB_WMosgG-8W7eLePJ42PwWQvLiQx16Pls052VqwHO7tKm-_u5AnWly0ewkNiMkxn-AjQb1JI,&typo=1>
>>
>>
>>
>>
>>
>>
>>
>> *From:* Fpdcdesign <[email protected]>
>> *Sent:* Thursday, September 1, 2022 6:58 AM
>> *To:* Discussion list on issues relating to automatic fire sprinklers <
>> [email protected]>
>> *Subject:* [Sprinklerforum] Intumescent Paint
>>
>>
>>
>> Has anyone dealt with a situation where an intumescent paint has been
>> used on a wood structure to make a space above a ceiling non combustible?
>> I’ve never been a fan of this stuff but I have a building owner that is
>> adamant about using it.
>>
>>
>>
>> Todd G Williams, PE
>>
>> Fire Protection Design/Consulting
>>
>> Stonington, CT
>>
>> 860-535-2080 (ofc)
>>
>> 860-554-7054  (fax)
>>
>> 860-608-4559 (cell)
>>
>> _________________________________________________________
>> SprinklerForum mailing list:
>>
>> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
>> To unsubscribe send an email to
>> [email protected]
>
> --
> Bob Caputo, CFPS
> *President*
>
> *American Fire Sprinkler Association*
> p: 214-349-5965 ext124
> w: firesprinkler.org
> <https://www.facebook.com/firesprinkler.org/>
> <https://twitter.com/afsa/status/1039528345367732224>
> <https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
>    <https://www.instagram.com/firesprinklerorg/>
>
> *Train a safer, more efficient workforce.*
>
> By enrolling your employees in the AFSA Apprenticeship Training Series
> for Sprinkler Fitters
> <https://www.firesprinkler.org/WWW/Education/Apprentice_Training/WWW/Education/Apprenticeship_Training.aspx?hkey=e88ef09e-d74c-407f-abcd-995aff866149>,
> you will reap the benefits of a qualified, professional installation crew.
> Well-trained employees will work smarter, increasing your company's
> productivity and, in turn, its profits. Learn more
> <https://www.firesprinkler.org/WWW/Education/Apprentice_Training/WWW/Education/Apprenticeship_Training.aspx?hkey=e88ef09e-d74c-407f-abcd-995aff866149>
> .
> _________________________________________________________ SprinklerForum
> mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to