It is important to inquire about the actual intended use of the facility.
A few scenarios have come up that are similar in description to the hazard
that you have only to find out after the installation that it is rented out
for events on off-hours to be regularly filled up with bounce houses, food
trucks, or other hazards that may need to be considered upon hazard
analysis.  Though it is not possible to predict the owner's intent or all
of the possibilities the increase of plastic may need to be considered upon
hazard analysis.

The above is my opinion and has not been processed as a formal
interpretation in accordance with the NFPA Regulations Governing Committee
Projects. This is provided with the understanding that the AFSA assumes no
liability for this opinion or actions taken on it and they are not to be
considered the official position of the NFPA or its technical committees.
AFSA cannot provide design or consulting engineering services, and this
opinion should therefore not be considered, nor relied upon, as such.

On Mon, Feb 7, 2022 at 8:17 AM Prahl, Craig/GVL via Sprinklerforum <
[email protected]> wrote:

> Take it a step farther.  You need to look at all the various areas within
> the building.  For multi-use buildings, you can have various levels of
> hazards under one roof.  This is one reason why you can't use the annex as
> an end-all of occupancies.
>
>
>
> Tall, open areas need to be looked at differently than standard height
> 8-10 ft areas.
>
>
>
> Look at your sprinkler listings. A sprinkler Listed for LH may have a
> ceiling height limitation.
>
>
>
> Don't ya just love the wild and wooly world of fire protection?  😊
>
>
>
> Craig Prahl | Jacobs | Group Lead/SME – Fire Protection |
> [email protected] | www.jacobs.com
>
> 1041 East Butler Road   Greenville, South Carolina  29606
>
> CONTACT BY: email or MS TEAMS
>
>
>
>
>
>
>
> -----Original Message-----
> From: Sprinklerforum <[email protected]> On
> Behalf Of Bob Caputo via Sprinklerforum
> Sent: Monday, February 7, 2022 8:58 AM
> To: [email protected]
> Cc: Bob Caputo <[email protected]>; [email protected]
> Subject: [EXTERNAL] RE: INDOOR SPORTS FACILITY FIELD HOUSE
>
>
>
> Not in my opinion.  We should always look at the definitions for each
> occupancy classification as opposed to the list in the annex.  These
> facilities have a lot of plastics and combustibles that exceed the
> definition of light hazard and they are of heights exceeding 8 ft so OH1 is
> probably not adequate.
>
>
>
> When I look at the foam in landing pits of gymnasiums or even the
> bleachers, I'd have a hard time seeing a simple gymnasium as light hazard.
>
>
>
> This is a personal opinion.
>
>
>
> Bob Caputo, CFPS
>
> President
>
> American Fire Sprinkler Association
>
>
>
>
>
> -----Original Message-----
>
> From: Sprinklerforum <[email protected]
> <mailto:[email protected]>> On Behalf Of
> tstone52--- via Sprinklerforum
>
> Sent: Monday, February 7, 2022 7:44 AM
>
> To: [email protected]<mailto:
> [email protected]>
>
> Cc: [email protected]<mailto:[email protected]>
>
> Subject: INDOOR SPORTS FACILITY FIELD HOUSE
>
>
>
> NFPA does not define Field houses.
>
>
>
> Indoor Track, Basketball Courts, Tennis Courts and Climbing Wall. The new
> building will be 37'-0 high to the peak of a flat roof.
>
>
>
>
>
>
>
> Would it be safe to use Light Hazard Occupancy?
>
>
>
>
>
>
>
>
>
>
>
> Regards,
>
>
>
> G. Tim Stone
>
>
>
>
>
>
>
> G. Tim Stone Consulting, LLC
>
>
>
> NICET Level III Engineering Technician
>
>
>
> Fire Protection Sprinkler Design
>
>
>
> and Consulting Services
>
>
>
>
>
>
>
>    117 Old Stage Rd. - Essex Jct., VT. 05452
>
>
>
>                  CELL: (802) 373-0638
>
>
>
>               <mailto:[email protected]> [email protected]<mailto:
> [email protected]>
>
>
>
>
>
>
>
> _______________________________________________
>
> Sprinklerforum mailing list
>
> [email protected]<mailto:
> [email protected]>
>
>
> https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o__;!!B5cixuoO7ltTeg!ST2dG3hqxRkvBw-dzx61kx0gBeM41Dd__thMJ_eFqHAjzCxZygMolAa1ML5_7cG_uA$
> <
> https://urldefense.com/v3/__http:/lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o__;!!B5cixuoO7ltTeg!ST2dG3hqxRkvBw-dzx61kx0gBeM41Dd__thMJ_eFqHAjzCxZygMolAa1ML5_7cG_uA$
> >
>
> rg
>
> _______________________________________________
>
> Sprinklerforum mailing list
>
> [email protected]<mailto:
> [email protected]>
>
>
> https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!ST2dG3hqxRkvBw-dzx61kx0gBeM41Dd__thMJ_eFqHAjzCxZygMolAa1ML4wgnIYqQ$
> <
> https://urldefense.com/v3/__http:/lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!ST2dG3hqxRkvBw-dzx61kx0gBeM41Dd__thMJ_eFqHAjzCxZygMolAa1ML4wgnIYqQ$
> >
>
> ________________________________
>
> NOTICE - This communication may contain confidential and privileged
> information that is for the sole use of the intended recipient. Any
> viewing, copying or distribution of, or reliance on this message by
> unintended recipients is strictly prohibited. If you have received this
> message in error, please notify us immediately by replying to the message
> and deleting it from your computer.
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>


-- 
*Best Regards,*


Josh McDonald, MSET, CFPS
Technical Programs Specialist

*American Fire Sprinkler Association*
p: 214-349-5965 ext. 138
w: firesprinkler.org
<https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/afsa/status/1039528345367732224>
<https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
   <https://www.instagram.com/firesprinklerorg/>

Expand your design department in 2022!

Learn design with AFSA's Beginning Fire Sprinkler System Planning School.
Our technical experts teach the basics of system layout based on the 2019
edition of NFPA 13. Space is limited. Enroll today at:
www.firesprinkler.org/schools.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to