Not in my opinion.  We should always look at the definitions for each
occupancy classification as opposed to the list in the annex.  These
facilities have a lot of plastics and combustibles that exceed the
definition of light hazard and they are of heights exceeding 8 ft so OH1
is probably not adequate.

When I look at the foam in landing pits of gymnasiums or even the
bleachers, I'd have a hard time seeing a simple gymnasium as light hazard.

This is a personal opinion.

Bob Caputo, CFPS
President
American Fire Sprinkler Association


-----Original Message-----
From: Sprinklerforum <[email protected]> On
Behalf Of tstone52--- via Sprinklerforum
Sent: Monday, February 7, 2022 7:44 AM
To: [email protected]
Cc: [email protected]
Subject: INDOOR SPORTS FACILITY FIELD HOUSE

NFPA does not define Field houses.

Indoor Track, Basketball Courts, Tennis Courts and Climbing Wall. The new
building will be 37'-0 high to the peak of a flat roof.



Would it be safe to use Light Hazard Occupancy?





Regards,

G. Tim Stone