They reference section 1026.6

1026.6 Exterior stairway and ramp protection. Exterior exit stairways and
ramps shall be separated from the interior of the building as required in
Section 1022.2. Openings shall be limited to those necessary for egress from
normally occupied spaces.

And in particular Exception #4

4. Separation from the interior of the building is not required for exterior
stairways or ramps connected to open-ended corridors, provided that Items
4.1 through 4.5 are met:

        4.1. The building, including corridors, stairways or ramps, shall be
equipped throughout with an automatic sprinkler system in
        accordance with Section 903.3.1.1 (NFPA 13) or 903.3.1.2. (NPFA 13R)

Thanks,






Dane Long, AET
Engineering Technician | Bamford Fire Sprinkler Co., Inc.
P:    785.825.7710
F:    785.825.0667
A:   1383 W. North Street  Salina, KS  67401



-----Original Message-----
From: Sprinklerforum <[email protected]> On
Behalf Of Mike Morey via Sprinklerforum
Sent: Thursday, January 6, 2022 11:43 AM
To: [email protected]
Cc: Mike Morey <[email protected]>
Subject: RE: Open or exterior corridors

What in the IBC is requiring this, the only difference I'm aware of (which
is no longer a difference at least in the last cycle or two) is that Type V
construction requires protection of porch/patio/decks.  I don't believe an
exit corridor falls within those requirements?  The intent was to counteract
patio heaters/grills etc as a potential ignition source.

Mike Morey
CFPS 3229 . NICET S.E.T. 123677
Project Manager . Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive . Fort Wayne, IN . 46825 direct 260.487.7824 /  cell
260.417.0625 /  fax 260.487.7991 email [email protected]



-----Original Message-----
From: Sprinklerforum <[email protected]> On
Behalf Of Dane Long via Sprinklerforum
Sent: Thursday, January 6, 2022 12:38 PM
To: [email protected]
Cc: Dane Long <[email protected]>
Subject: Open or exterior corridors

 
BE ADVISED - This email originated outside EMCOR. 
 

I have a 13R project with exterior open corridors as seen in 13R (2016)
Figure A.6.6.5(a). Per the IBC were being required to provide protection.

Can I apply 6.6.5.1.1?

6.6.5.1.1 Where sidewall sprinklers are installed beneath decks or balconies
constructed with open wood joists, sprinklers shall be permitted to be
installed with deflectors not less than 1 in. (25 mm) or more than 6 in.
(152 mm) below the structural members, provided that the deflector is not
more than 14 in. (356 mm) below the underside surface of the deck.

If so, does this restrict me from using EC head, since 13R only says
"sidewall sprinklers" and since it's a combustible obstructed construction?
Therefore, requiring a smooth flat ceiling.

Thanks for your help in advance,

Dane Long, AET
Engineering Technician | Bamford Fire Sprinkler Co., Inc.
P:    785.825.7710
F:    785.825.0667
A:   1383 W. North Street  Salina, KS  67401



-----Original Message-----
From: Sprinklerforum <[email protected]> On
Behalf Of Prahl, Craig/GVL via Sprinklerforum
Sent: Wednesday, January 5, 2022 9:14 AM
To: [email protected]
Cc: Prahl, Craig/GVL <[email protected]>; Matt Grise
<[email protected]>; Kevin Hall <[email protected]>
Subject: RE: Thread connection holding on one thread only

The depth of engagement to form a leakproof connection is dependent on the
pipe diameter and system pressure.

For general talking purposes per ASME B1.20.1, for NPT pipes, a 1.25" pipe
is shown as having 11.5 threads per inch with the typical hand tightening
limitation at 4.5 turns for a depth of 0.42 inches (<5 threads).  Past that
to get to full engagement requires the use of a wrench.  Effective length of
thread is shown as 0.707 inches.

So it's amazing that with only two threads for engagement it didn't come
apart under the pressure test and stayed in place for 15 years. I would
wonder if there are any other connections in a similar condition.

Craig Prahl | Jacobs | Group Lead/SME - Fire Protection |
[email protected] |
https://urldefense.com/v3/__http://www.jacobs.com__;!!FaxH778!JByPw1WZ48LniB
41DIoIfiJnySXCbZVFT8QpxPa9WEP920iNA-egD4MiEYOmc_KT$ 
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: email or MS TEAMS



-----Original Message-----
From: Sprinklerforum <[email protected]> On
Behalf Of Matt Grise via Sprinklerforum
Sent: Wednesday, January 5, 2022 9:42 AM
To: [email protected]
Cc: Matt Grise <[email protected]>; Kevin Hall <[email protected]>
Subject: [EXTERNAL] RE: Thread connection holding on one thread only

If I recall from my book-learning days, there is a pretty well established
minimum thread engagement that provides the full strength of a threaded
connection. (maybe 3?). That may also only apply to bolts though.

Matt


-----Original Message-----
From: Sprinklerforum <[email protected]> On
Behalf Of Kevin Hall via Sprinklerforum
Sent: Wednesday, January 05, 2022 8:33 AM
To: [email protected]
Cc: Kevin Hall <[email protected]>
Subject: Re: Thread connection holding on one thread only

I do not believe one is sufficient. I recall a project where the
specification limited the maximum number of exposed threads to 2 or 3. I'd
have to do some research to find the product/installation standard that was
referenced.


Kevin Hall, M.Eng., P.E., ET, CWBSP, PMSFPE

Coordinator, Engineering and Technical Services

American Fire Sprinkler Association

[email protected]

214-349-5971


On Wed, Jan 5, 2022 at 2:16 AM Dan Arbel via Sprinklerforum <
[email protected]> wrote:

> Dear Forum Members
>
> I have a case where 1.25" NPT pipe nipple was connected to 1.25" BSP 
> (as per British standard) pipe.
>
> Sprinkler System in interstitial space.
>
> There was only 2 threads engagement.
>
> After about 15 years somebody touched the a pipe and the connection 
> disengaged.
>
> I would appreciated the members opinion on the allegation that even 
> one thread engagement is sufficient providing sufficient strength.
>
> Dan Arbel
> Dan Arbel Risk Engineering Ltd
> Mail: [email protected]
> WEB SITE:
> https://urldefense.com/v3/__https://linkprotect.cudasvc.com/url?a=http
> s*3a*2f*2fwww.riskmanage.com__;JSUl!!B5cixuoO7ltTeg!XkU8cH2TMBKLQ2ZlRo
> 1tisvmulk98nUEHNhgQ5Y2N2mjqKrtgbiQDgiMg-yghiPIMw$
> &c=E,1,rOBCJWaUiWX-Zi-j03j48v-ojODJ4zDjCTCn-XcTQUWSVSZzQRanv2vrdqlUogX
> nkOECEYOqMT2eMuzN6PVEfyuVyVF6Hoz4BiV1VyGvBRCcljgZH2U,&typo=1
> Mobile: +972-52-6611337
> Tel: +972-4-8243337
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> https://urldefense.com/v3/__https://linkprotect.cudasvc.com/url?a=http
> *3a*2f*2flists.firesprinkler__;JSUl!!B5cixuoO7ltTeg!XkU8cH2TMBKLQ2ZlRo
> 1tisvmulk98nUEHNhgQ5Y2N2mjqKrtgbiQDgiMg-zXS7SC2A$
> .org%2flistinfo.cgi%2fsprinklerforum-firesprinkler.org&c=E,1,RvPpy3ldS
> C8kzu280ouAOq2QKBzNGfMu7REiocN-XOdCtouKzXB4EaUtnbHa1UoPns-R2H1fzQj-fW-
> oIX3YW0Doh9ZL84fg3cNaQ0q1OQ,,&typo=1
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.com/v3/__https://linkprotect.cudasvc.com/url?a=http*3a*2f
*2flists.firesprinkler.org*2flistinfo.cgi*https://urldefense.com/v3/__http:/
/2fsprinklerforum-firesprinkler.org__;!!FaxH778!JByPw1WZ48LniB41DIoIfiJnySXC
bZVFT8QpxPa9WEP920iNA-egD4MiEU7a5TFY$
&c=E,1,wikZY07kLJSV87o86Ivs1Jsxm4l75jKdQbbfbZ7tVZifvQRGY33Wh20_IAQ7wACFTF9yF
LpxM-xqELTjxDST6UJ7dCl0WTqJP_LkvfP8qA,,&typo=1__;JSUlJSU!!B5cixuoO7ltTeg!XkU
8cH2TMBKLQ2ZlRo1tisvmulk98nUEHNhgQ5Y2N2mjqKrtgbiQDgiMg-w4GyP2OA$
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/spri
nklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!XkU8cH2TMBKLQ2ZlRo1tisvmulk9
8nUEHNhgQ5Y2N2mjqKrtgbiQDgiMg-w8lV3Y3w$

________________________________

NOTICE - This communication may contain confidential and privileged
information that is for the sole use of the intended recipient. Any viewing,
copying or distribution of, or reliance on this message by unintended
recipients is strictly prohibited. If you have received this message in
error, please notify us immediately by replying to the message and deleting
it from your computer.
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/spri
nklerforum-firesprinkler.org__;!!FaxH778!JByPw1WZ48LniB41DIoIfiJnySXCbZVFT8Q
pxPa9WEP920iNA-egD4MiEYiB_lJs$ 

_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/spri
nklerforum-firesprinkler.org__;!!FaxH778!JByPw1WZ48LniB41DIoIfiJnySXCbZVFT8Q
pxPa9WEP920iNA-egD4MiEYiB_lJs$ 

This message is for the named person's use only.  It may contain
confidential, proprietary or legally privileged information. No
confidentiality or privilege is waived or lost by any mistransmission.  If
you receive this message in error, please  immediately delete it and all
copies of it from your system, destroy any hard copies of it and notify the
sender.  You must not, directly or indirectly, use, disclose, distribute,
print, or copy any part of this message if you are not the intended
recipient.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to