You will have to put ESFR sprinklers under the 30" wide duct as it is over 24" 
wide. As for the 24" wide duct, the ESFR sprinkler heads need to be at least 
2'-0" horizontally from the edge of the duct. If the 24" duct is unable to be 
moved, then you will either have to put heads under it as well. 


TYSON SUTHERLAND, CET
NICET Level III Design Technician
Ohio ASSD #8495

2900 Newpark Drive
Barberton, OH 44203

888-857-2817 x317
330-600-0697 Cell
[email protected]

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Fpdcdesign via Sprinklerforum
Sent: Thursday, December 9, 2021 2:36 PM
To: Sprinklerforum <[email protected]>
Cc: Fpdcdesign <[email protected]>
Subject: Obstructions below ESFR sprinklers

 
BE ADVISED - This email originated outside EMCOR. 
 

      
  

  I am working on a project with an ESFR system and we have some ductwork 
installed below it. The duct system is T shaped with 24” wide section 50 ft 
long and 30” wide section 12’-6” long protruding from the center of the 24”. 
The top of the duct is 3’-8” below the sprinkler deflector. Section 8.12 (2013 
edition) is kind of vague on obstruction distances below the ESFR sprinklers. 
Does anyone have any insight or experience that they would like to share on 
this? Thanks.
  
  
  
 Todd G Williams, PE  
Fire Protection Design/Consulting
  
Stonington, CT
  
860-535-2080 (tel:860-535-2080)  (ofc)
  
860-554-7054 (tel:860-554-7054)     (fax)
  
860-608-4559 (tel:860-608-4559)  (cell)
  
  
  
  

  
     
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!FaxH778!LFCQj51g2L3rbuSbKQquxmREP8zAE0A9cMyjgfHDdt5LnnlzuyYd15W7p1qGDJpaYTHkqm8$
 

This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to