For what it is worth, we went in a different direction.  We upsized the jockey 
pump to 50gpm to handle the flow of one sprinkler (5.6 X square root of 100) so 
that testing of the sprinkler switches can be done without the booster pump 
operating (we often have lots of switches supplied by the pump).  This allows a 
lot of switches to be tested without having to shut down the pump, which would 
require instituting impairment procedures.  We also generally use manual shut 
down for the booster pump upon activation of the pump running alarm and staff 
who would respond to the pump don't have to be involved during switch testing 
with this arrangement.

Pete Larrimer
VA  

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of BF Blake via Sprinklerforum
Sent: Thursday, November 18, 2021 3:27 PM
To: [email protected]
Cc: BF Blake <[email protected]>
Subject: [EXTERNAL] Re: Fire Pump Shutdown

Copy.  Was installed/designed to 2013 Edition.  Central station reporting is 
not operational.  Thanks for all.

Byron

________________________________
From: Sprinklerforum <[email protected]> on behalf 
of John Denhardt via Sprinklerforum <[email protected]>
Sent: Thursday, November 18, 2021 11:23 PM
To: [email protected] 
<[email protected]>
Cc: John Denhardt <[email protected]>
Subject: Re: Fire Pump Shutdown

Keep in mind the following from UFC 3-600-01 (8 AUGUST 2016, CHANGE 5, 14 
SEPTEMBER 2020)

9.5.3 Pump Start and Shutdown.


9.5.3.1 Fire pumps must be arranged to start automatically.


9.5.3.2 Fire pumps must be arranged to automatically shut down after reaching 
the

stop pressure and the expiration of \3\the minimum run time determined by NFPA 
20/3/.

Stop pressure must be at least 5 psi below maximum churn pressure at the lowest

available static pressure.

Note: The lowest available static pressure should be utilized in determining 
churn

pressure so that the stop pressure can be achieved with low pressure. The 5 psi

differential is used to allow for gauge error.\2\


9.5.3 /2/Fire pump activation (run) must transmit an alarm condition to the

Installation receiving station, or remote receiving station, but not activate 
the Facility

notification appliance


While I understand what the above states, my personal opinion is to have the 
fire pump operating anytime a sprinkler is operating.  We do not want to short 
cycle the fire pump.  My suggestion is always for manual shut-down unless the 
site is unmanned and response to the site would take considerable time..  A 
properly designed and maintained fire pump system can operate at churn or near 
churn conditions for a lengthy time with no issues.

We all know fire pump systems are maintained in full accordance with NFPA
25 and the manufacturer's recommendations.

*The above is my opinion and has not been processed as a formal interpretation 
in accordance with the NFPA Regulations Governing Committee Projects. This is 
provided with the understanding that the AFSA assumes no liability for this 
opinion or actions taken on it and they are not to be considered the official 
position of the **AFSA, and/or NFPA or its technical committees.**AFSA cannot 
provide design or consulting engineering services, and this opinion should 
therefore not be considered, nor relied upon, as such.*

Thanks,
John

John August Denhardt, PE
*Vice President, Engineering and Technical Services*

*American Fire Sprinkler Association*
m: p: 301-343-1457
214-349-5965 ext 121
w: firesprinkler.org
<https://gcc02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2Ffiresprinkler.org%2F&amp;data=04%7C01%7C%7Ce77f82920c1b4121c81a08d9aad1d7b5%7Ce95f1b23abaf45ee821db7ab251ab3bf%7C0%7C0%7C637728640517024173%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=4hbQHFn9YeX0dIc%2BpnuDhI%2FF8VZ%2BuOKy4lS%2BEps5YeU%3D&amp;reserved=0>
<https://gcc02.safelinks.protection.outlook.com/?url=https%3A%2F%2Ftwitter.com%2Fafsa%2Fstatus%2F1039528345367732224&amp;data=04%7C01%7C%7Ce77f82920c1b4121c81a08d9aad1d7b5%7Ce95f1b23abaf45ee821db7ab251ab3bf%7C0%7C0%7C637728640517024173%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=YSJggNp%2FvC7udgb4OBJXGYNCwxHSgIdla%2B0jn3V%2F%2FH4%3D&amp;reserved=0>
<https://gcc02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fcompany%2Famerican-fire-sprinkler-association-afsa-%2F&amp;data=04%7C01%7C%7Ce77f82920c1b4121c81a08d9aad1d7b5%7Ce95f1b23abaf45ee821db7ab251ab3bf%7C0%7C0%7C637728640517024173%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=EWdjjWzFysZjrSl0gu3yQPdXUn9MwyCIrQu4U7IFEoY%3D&amp;reserved=0>
   
<https://gcc02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.instagram.com%2Ffiresprinklerorg%2F&amp;data=04%7C01%7C%7Ce77f82920c1b4121c81a08d9aad1d7b5%7Ce95f1b23abaf45ee821db7ab251ab3bf%7C0%7C0%7C637728640517024173%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=oVAv1fuHAtsv8VXnbSwHc%2B2j2I%2BX0ZlrjxTLOJt56W8%3D&amp;reserved=0>

*Our members are at the heart of everything we do.*


*Are you a member with a technical question? *

Don't forget one of the most valuable resources that American Fire Sprinkler 
Association provides is technical reviews from our Engineering & Technical 
Services Department. It's like having an FPE on your staff. Visit
https://gcc02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.firesprinkler.org%2Finterp&amp;data=04%7C01%7C%7Ce77f82920c1b4121c81a08d9aad1d7b5%7Ce95f1b23abaf45ee821db7ab251ab3bf%7C0%7C0%7C637728640517024173%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=CZLoiuIGHeyOmtS6LZwg7T4EBT1OL39bqq8vmmqS3LM%3D&amp;reserved=0
<https://gcc02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.firesprinkler.org%2FWWW%2FContacts%2FSign_In.aspx%3FWebsiteKey%3D3dff22a3-0306-479c-bccc-7aa1986c8ada%26LoginRedirect%3Dtrue%26returnurl%3D%2FWWW%2FTechnical_Services%2FInformal_Interpretations%2FWWW%2FInformal_Interpret%2FMember_View.aspx%3Fhkey%3D8023e65f-a2ad-4465-9920-0f9313a07324&amp;data=04%7C01%7C%7Ce77f82920c1b4121c81a08d9aad1d7b5%7Ce95f1b23abaf45ee821db7ab251ab3bf%7C0%7C0%7C637728640517024173%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=6sIc%2FvF3CNOcknTm47sVubYFAKT0WH2hUynTv8%2FF2AY%3D&amp;reserved=0>
to
submit a question today!



On Thu, Nov 18, 2021 at 3:13 PM BF Blake via Sprinklerforum < 
[email protected]> wrote:

> Thanks John, 100% with you.
> Byron, Poland.
>
>
> ________________________________
> From: Sprinklerforum <[email protected]> 
> on behalf of John Denhardt via Sprinklerforum < 
> [email protected]>
> Sent: Thursday, November 18, 2021 11:11 PM
> To: [email protected] < 
> [email protected]>
> Cc: John Denhardt <[email protected]>
> Subject: Re: Fire Pump Shutdown
>
> To me, the intent is to have the fire pump operating anytime a 
> sprinkler is operating.  We do not want to short cycle the fire pump.  
> My suggestion is always for manual shut-down unless the site is 
> unmanned and response to Technical he site would take considerable 
> time..  A properly designed and maintained fire pump system can 
> operate at churn or near churn conditions for a lengthy time with no issues.
>
> *The above is my opinion and has not been processed as a formal 
> interpretation in accordance with the NFPA Regulations Governing 
> Committee Projects. This is provided with the understanding that the 
> AFSA assumes no liability for this opinion or actions taken on it and 
> they are not to be considered the official position of the **AFSA, 
> and/or NFPA or its technical committees.**AFSA cannot provide design 
> or consulting engineering services, and this opinion should therefore 
> not be considered, nor relied upon, as such.*
>
> Thanks,
> John
>
> John August Denhardt, PE
> *Vice President, Engineering and Technical Services*
>
> *American Fire Sprinkler Association*
> m: p: 301-343-1457
> 214-349-5965 ext 121
> w: firesprinkler.org
> <
> https://gcc02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.
> facebook.com%2Ffiresprinkler.org%2F&amp;data=04%7C01%7C%7Ce77f82920c1b
> 4121c81a08d9aad1d7b5%7Ce95f1b23abaf45ee821db7ab251ab3bf%7C0%7C0%7C6377
> 28640517024173%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2l
> uMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=4hbQHFn9YeX0dIc%2
> BpnuDhI%2FF8VZ%2BuOKy4lS%2BEps5YeU%3D&amp;reserved=0
> >
> <
> https://gcc02.safelinks.protection.outlook.com/?url=https%3A%2F%2Ftwit
> ter.com%2Fafsa%2Fstatus%2F1039528345367732224&amp;data=04%7C01%7C%7Ce7
> 7f82920c1b4121c81a08d9aad1d7b5%7Ce95f1b23abaf45ee821db7ab251ab3bf%7C0%
> 7C0%7C637728640517024173%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiL
> CJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=YSJggNp
> %2FvC7udgb4OBJXGYNCwxHSgIdla%2B0jn3V%2F%2FH4%3D&amp;reserved=0
> >
> <
> https://gcc02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.
> linkedin.com%2Fcompany%2Famerican-fire-sprinkler-association-afsa-%2F&
> amp;data=04%7C01%7C%7Ce77f82920c1b4121c81a08d9aad1d7b5%7Ce95f1b23abaf4
> 5ee821db7ab251ab3bf%7C0%7C0%7C637728640517024173%7CUnknown%7CTWFpbGZsb
> 3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%
> 7C3000&amp;sdata=EWdjjWzFysZjrSl0gu3yQPdXUn9MwyCIrQu4U7IFEoY%3D&amp;re
> served=0
> >
>    <
> https://gcc02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.
> instagram.com%2Ffiresprinklerorg%2F&amp;data=04%7C01%7C%7Ce77f82920c1b
> 4121c81a08d9aad1d7b5%7Ce95f1b23abaf45ee821db7ab251ab3bf%7C0%7C0%7C6377
> 28640517024173%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2l
> uMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=oVAv1fuHAtsv8VXnb
> SwHc%2B2j2I%2BX0ZlrjxTLOJt56W8%3D&amp;reserved=0
> >
>
> *Our members are at the heart of everything we do.*
>
>
> *Are you a member with a technical question? *
>
> Don't forget one of the most valuable resources that American Fire 
> Sprinkler Association provides is technical reviews from our 
> Engineering & Technical Services Department. It's like having an FPE 
> on your staff. Visit
>
> https://gcc02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.f
> iresprinkler.org%2Finterp&amp;data=04%7C01%7C%7Ce77f82920c1b4121c81a08
> d9aad1d7b5%7Ce95f1b23abaf45ee821db7ab251ab3bf%7C0%7C0%7C63772864051702
> 4173%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBT
> iI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=CZLoiuIGHeyOmtS6LZwg7T4EBT1
> OL39bqq8vmmqS3LM%3D&amp;reserved=0
> <
> https://gcc02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.
> firesprinkler.org%2FWWW%2FContacts%2FSign_In.aspx%3FWebsiteKey%3D3dff2
> 2a3-0306-479c-bccc-7aa1986c8ada%26LoginRedirect%3Dtrue%26returnurl%3D%
> 2FWWW%2FTechnical_Services%2FInformal_Interpretations%2FWWW%2FInformal
> _Interpret%2FMember_View.aspx%3Fhkey%3D8023e65f-a2ad-4465-9920-0f9313a
> 07324&amp;data=04%7C01%7C%7Ce77f82920c1b4121c81a08d9aad1d7b5%7Ce95f1b2
> 3abaf45ee821db7ab251ab3bf%7C0%7C0%7C637728640517024173%7CUnknown%7CTWF
> pbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6M
> n0%3D%7C3000&amp;sdata=6sIc%2FvF3CNOcknTm47sVubYFAKT0WH2hUynTv8%2FF2AY
> %3D&amp;reserved=0
> >
> to
> submit a question today!
>
>
> On Thu, Nov 18, 2021 at 2:27 PM BF Blake via Sprinklerforum < 
> [email protected]> wrote:
>
> > Greetings Forum Members
> >
> > Do we believe it is the intent of NFPA 20 TC is  for 10 minute 
> > automatic shut down (when enabled) of fire pumps to apply only during churn 
> > (e.g.
> > dead head, closed loop, testing) conditions or to any condition to
> include
> > sprinkler flow (e.g. 1/2" 5.6K ITC flow)?
> >
> > Is the intent to protect the fire pump from "burn out"?  Is the 
> > intent to run pumps to failure (destruction) or is the intent, with 
> > 10 minute auto shut down, where permitted, to attempt to preserve the pump?
> >
> > Thanks
> >
> > Byron
> > NATO Facility
> > UFC Criteria 03-600-01 (2013) Applicable Słupsk, Pomorskie, Poland
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> >
> https://gcc02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists
> .firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&a
> mp;data=04%7C01%7C%7Ce77f82920c1b4121c81a08d9aad1d7b5%7Ce95f1b23abaf45
> ee821db7ab251ab3bf%7C0%7C0%7C637728640517034132%7CUnknown%7CTWFpbGZsb3
> d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7
> C3000&amp;sdata=Y1iTfH2ifJnALm%2FwsFqNs%2BujWt6N4H2p2he4xP74xaA%3D&amp
> ;reserved=0
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> https://gcc02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists
> .firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&a
> mp;data=04%7C01%7C%7Ce77f82920c1b4121c81a08d9aad1d7b5%7Ce95f1b23abaf45
> ee821db7ab251ab3bf%7C0%7C0%7C637728640517034132%7CUnknown%7CTWFpbGZsb3
> d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7
> C3000&amp;sdata=Y1iTfH2ifJnALm%2FwsFqNs%2BujWt6N4H2p2he4xP74xaA%3D&amp
> ;reserved=0 _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> https://gcc02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists
> .firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&a
> mp;data=04%7C01%7C%7Ce77f82920c1b4121c81a08d9aad1d7b5%7Ce95f1b23abaf45
> ee821db7ab251ab3bf%7C0%7C0%7C637728640517034132%7CUnknown%7CTWFpbGZsb3
> d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7
> C3000&amp;sdata=Y1iTfH2ifJnALm%2FwsFqNs%2BujWt6N4H2p2he4xP74xaA%3D&amp
> ;reserved=0
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://gcc02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&amp;data=04%7C01%7C%7Ce77f82920c1b4121c81a08d9aad1d7b5%7Ce95f1b23abaf45ee821db7ab251ab3bf%7C0%7C0%7C637728640517034132%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=Y1iTfH2ifJnALm%2FwsFqNs%2BujWt6N4H2p2he4xP74xaA%3D&amp;reserved=0
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://gcc02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&amp;data=04%7C01%7C%7Ce77f82920c1b4121c81a08d9aad1d7b5%7Ce95f1b23abaf45ee821db7ab251ab3bf%7C0%7C0%7C637728640517034132%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=Y1iTfH2ifJnALm%2FwsFqNs%2BujWt6N4H2p2he4xP74xaA%3D&amp;reserved=0
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to