Mike,

Thanks

In my case I can operate the ITC and get JP and FP to start, then FP stops at 
10 minutes with the 1/2" still open and flowing.

The ITC calculated flow is 70 GPM, the FP is 1250 GPM.  Central station 
reporting is NOT operational here, but that is a side note.

FP will not auto restart unless I open more heads, which in a real world fire 
scenario is exacrly what will happen

This is designed under 2013 UFC 03-600-01.

Thank You Sir.

Byron

________________________________
From: Sprinklerforum <[email protected]> on behalf 
of Mike Morey via Sprinklerforum <[email protected]>
Sent: Thursday, November 18, 2021 10:38 PM
To: [email protected] 
<[email protected]>
Cc: Mike Morey <[email protected]>
Subject: RE: Fire Pump Shutdown

I've always understood it to be allowed even for a non-testing situation if 
approved.  The 2019 edition clarified this somewhat by breaking out automated 
testing as essentially ok even without specific approval and then a separate 
line item for when approved by the AHJ.  In places where the pump may not 
readily get shut off during an accidental start the 10 minute timer makes a lot 
of sense.  Timer only starts when shutoff pressure is reached and start 
pressure isn't dropped below again for 10 minutes, and even then pump would 
immediately restart if pressure dropped again.  I've always felt we were pretty 
conservative in how rarely it's utilized.

Mike Morey
CFPS 3229 . NICET S.E.T. 123677
Project Manager . Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive . Fort Wayne, IN . 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]



-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of BF Blake via Sprinklerforum
Sent: Thursday, November 18, 2021 2:27 PM
To: [email protected]
Cc: BF Blake <[email protected]>
Subject: Fire Pump Shutdown


BE ADVISED - This email originated outside EMCOR.


Greetings Forum Members

Do we believe it is the intent of NFPA 20 TC is  for 10 minute automatic shut 
down (when enabled) of fire pumps to apply only during churn (e.g. dead head, 
closed loop, testing) conditions or to any condition to include sprinkler flow 
(e.g. 1/2" 5.6K ITC flow)?

Is the intent to protect the fire pump from "burn out"?  Is the intent to run 
pumps to failure (destruction) or is the intent, with 10 minute auto shut down, 
where permitted, to attempt to preserve the pump?

Thanks

Byron
NATO Facility
UFC Criteria 03-600-01 (2013) Applicable Słupsk, Pomorskie, Poland

_______________________________________________
Sprinklerforum mailing list
[email protected]
https://emea01.safelinks.protection.outlook.com/?url=https%3A%2F%2Furldefense.com%2Fv3%2F__http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org__%3B!!FaxH778!OB4oaFijo2IZH9_K4Ka5cxdQY-nT0eZ81GZKqVwxU8Aeda74ceQbgz-mcJ3IOTAl%24&amp;data=04%7C01%7C%7Cf2648ec125f9440f235908d9aacb0a30%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637728611294808875%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=EZZRoWI6b6t76V0UlLXC2OcaVH%2FH34GSwuTYaMzniMA%3D&amp;reserved=0

This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://emea01.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&amp;data=04%7C01%7C%7Cf2648ec125f9440f235908d9aacb0a30%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637728611294808875%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=hWNBg1tc1HmbEF82%2BR6vESHmcaLBE3UaF1ECiqPBV7g%3D&amp;reserved=0
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to