The statement in 13 includes a pointer to what as in my understanding was the 
original intent, “on the same branch line leading back to the main”.  My 
understanding of this was the intent was to prevent having say a 80’ wide room 
as a remote area with a couple k11.2s then a couple k8.0 etc so that the 
increased node pressures from friction loss didn’t increase the discharge as 
you worked your way back to the main, squeezing pipe size.


Mike Morey

CFPS 3229 • NICET S.E.T. 123677

Project Manager • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company

7614 Opportunity Drive • Fort Wayne, IN • 46825

direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]

[Image]

________________________________
From: Sprinklerforum <[email protected]> on behalf 
of John Denhardt via Sprinklerforum <[email protected]>
Sent: Friday, October 29, 2021 10:45:38 AM
To: [email protected] 
<[email protected]>
Cc: John Denhardt <[email protected]>
Subject: Re: Mixing of K-Factors in self-storage facilities


BE ADVISED - This email originated outside EMCOR.


What K factor sprinkler are you trying to use?

John August Denhardt, P.E.
Vice-President Engineering and Technical Services
American Fire Sprinkler Association
301-343-1457

> On Oct 29, 2021, at 10:09 AM, Sean Lockyer via Sprinklerforum 
> <[email protected]> wrote:
>
> NFPA 13 generally discourages the use of mixing K-Factors in a system; 
> however, the mixing of K-Factors is allowed in certain circumstances, namely 
> in section 23.4.4.9.3 where it allows such use for small rooms and 
> enclosures. In a self-storage facility, the small 5' x 5' storage units would 
> not be considered "small rooms" as they are not light hazard (once again, per 
> the strict definition as layed out in chapter 3). However, would you be able 
> to consider the small units as enclosures since they are completely separate 
> rooms from the other, larger self-storage units ?
>
>             Sean Lockyer
>             Project Designer                            6817 N. Orange 
> Blossom Trail
>             Cell    386-337-1078                             Orlando, Florida 
> 32810
>             [email protected]             Phone:    407-816-9101
>             
> https://urldefense.com/v3/__http://www.AITLifeSafety.com__;!!FaxH778!Oy_jgPeRIlLfLOnvlyy99bOFdv8SJpLnbP2diyr4688tcb9BtnCFIJaqhbTElesa$
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!FaxH778!Oy_jgPeRIlLfLOnvlyy99bOFdv8SJpLnbP2diyr4688tcb9BtnCFIJaqhfoF0X8A$
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!FaxH778!Oy_jgPeRIlLfLOnvlyy99bOFdv8SJpLnbP2diyr4688tcb9BtnCFIJaqhfoF0X8A$

This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to