NFPA 13 generally discourages the use of mixing K-Factors in a system; however, 
the mixing of K-Factors is allowed in certain circumstances, namely in section 
23.4.4.9.3 where it allows such use for small rooms and enclosures. In a 
self-storage facility, the small 5' x 5' storage units would not be considered 
"small rooms" as they are not light hazard (once again, per the strict 
definition as layed out in chapter 3). However, would you be able to consider 
the small units as enclosures since they are completely separate rooms from the 
other, larger self-storage units ?

            Sean Lockyer
            Project Designer                            6817 N. Orange Blossom 
Trail
            Cell    386-337-1078                             Orlando, Florida 
32810
            [email protected]             Phone:    407-816-9101
            www.AITLifeSafety.com                  