The drywall makes no difference.  You could have 36" of concrete top and
bottom (I'm exaggerating), and it wouldn't matter.  This is because it
meets the definition of a combustible concealed space, so it must meet the
sprinkler requirements for a combustible concealed space.  Fires really do
happen in these spaces, and when they do, fire fighters have been injured
or died from the floor above collapsing on them, because they can't find
the fire to fight, despite smoke being everywhere.  The fire department
should be trained to look for this, but it still happens.  I'm glad you
asked the question, even if it has been asked before, because this is
important to get right.


Thanks,
Skyler Bilbo
Wente Plumbing and Fire Protection
1700 S. Raney Street
Effingham, IL 62401
217-819-6404 Direct
217-347-7315 Fax

[email protected]
www.wenteplumbing.com


On Fri, Oct 15, 2021 at 7:49 AM Brian Harris via Sprinklerforum <
[email protected]> wrote:

> Thank you. Does it make any difference if there's 2 layers of 5/8" Type X
> GWB on top and bottom?
>
> Brian Harris, CET
> BVS Systems Inc.
> bvssytemsinc.com
>
> -----Original Message-----
> From: Sprinklerforum <[email protected]> On
> Behalf Of Skyler Bilbo via Sprinklerforum
> Sent: Friday, October 15, 2021 8:37 AM
> To: [email protected]
> Cc: Skyler Bilbo <[email protected]>; Brian Harris <
> [email protected]>
> Subject: Re: Concealed Space Between Floors
>
> From the picture you sent, it looks like you have to install sprinklers.
>
> I think section 8.15.1 is what you are looking for (at least in the 2013 or
> 2016 editions).  The most common way I have seen to avoid installing
> sprinklers in this area is to fill it with noncombustible insulation.  If
> this was a NFPA 13R building, you would not need to install sprinklers in
> this space.  Be careful applying NFPA 13R to a building, as this is
> something the Architect/EOR must decide, and it depends on much more than
> if it is a residential building 4 stories or less in height.  Also, if you
> apply any of the rules that would omit sprinklers from 8.15.1, be sure to
> check 11.2.3.1.4 to see if you need to increase your design area(s) to
> 3,000 square feet.
>
>
> Thanks,
> Skyler Bilbo
> Wente Plumbing and Fire Protection
> 1700 S. Raney Street
> Effingham, IL 62401
> 217-819-6404 Direct
> 217-347-7315 Fax
>
> [email protected]
> www.wenteplumbing.com
>
>
> On Fri, Oct 15, 2021 at 7:25 AM Brian Harris via Sprinklerforum <
> [email protected]> wrote:
>
> > Hopefully this link works:
> > https://www.dropbox.com/s/526wgm341stybym/Floor%20Space.png?dl=0
> >
> > Brian Harris, CET
> > BVS Systems Inc.
> > bvssytemsinc.com
> >
> > -----Original Message-----
> > From: Sprinklerforum <[email protected]>
> > On Behalf Of Brian Harris via Sprinklerforum
> > Sent: Friday, October 15, 2021 8:23 AM
> > To: [email protected]
> > Cc: Brian Harris <[email protected]>
> > Subject: Concealed Space Between Floors
> >
> > I know this has been asked probably a million times but hopefully this
> > will be the last.
> > Does this space in a 13 system need to have sprinklers? (see attached)
> >
> >
> > Brian Harris, CET
> > BVS Systems Inc.
> > Design Manager
> > bvssystemsinc.com<http://bvssystemsinc.com/>
> > Phone: 704.896.9989
> > Fax: 704.896.1935
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to