It worked but I don't know that it shows enough detail to evaluate.  I'm 
guessing it's fabricated wood joists with open webs, metal channel with gyp 
board attached at the bottom.  In which case as is it would require protection, 
I believe the only non-sprinklered option would be (if it's "2 by" 
construction) fill all but the top 2" with insulation. (9.2.1.18, 13-2019).  
All other exceptions involve composite wood joists, the wood "I beam" if you 
will.

Mike Morey
CFPS 3229 * NICET S.E.T. 123677
Project Manager * Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive * Fort Wayne, IN * 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]



-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Brian Harris via Sprinklerforum
Sent: Friday, October 15, 2021 8:25 AM
To: [email protected]
Cc: Brian Harris <[email protected]>
Subject: RE: Concealed Space Between Floors

 
BE ADVISED - This email originated outside EMCOR. 
 

Hopefully this link works:
https://urldefense.com/v3/__https://www.dropbox.com/s/526wgm341stybym/Floor*20Space.png?dl=0__;JQ!!FaxH778!I8kXbi2qAeGP5ieQ1nj4zxmDkFkarn9E5Ri_Ko34WCfU6s4vQV3NaneMx6jmaWCf$
 

Brian Harris, CET
BVS Systems Inc.
https://urldefense.com/v3/__http://bvssytemsinc.com__;!!FaxH778!I8kXbi2qAeGP5ieQ1nj4zxmDkFkarn9E5Ri_Ko34WCfU6s4vQV3NaneMxyefx3fY$
 

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Brian Harris via Sprinklerforum
Sent: Friday, October 15, 2021 8:23 AM
To: [email protected]
Cc: Brian Harris <[email protected]>
Subject: Concealed Space Between Floors

I know this has been asked probably a million times but hopefully this will be 
the last.
Does this space in a 13 system need to have sprinklers? (see attached)


Brian Harris, CET
BVS Systems Inc.
Design Manager
https://urldefense.com/v3/__http://bvssystemsinc.com__;!!FaxH778!I8kXbi2qAeGP5ieQ1nj4zxmDkFkarn9E5Ri_Ko34WCfU6s4vQV3NaneMxw1k1AyJ$
 
<https://urldefense.com/v3/__http://bvssystemsinc.com/__;!!FaxH778!I8kXbi2qAeGP5ieQ1nj4zxmDkFkarn9E5Ri_Ko34WCfU6s4vQV3NaneMx-UhZJtW$
 >
Phone: 704.896.9989
Fax: 704.896.1935

_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!FaxH778!I8kXbi2qAeGP5ieQ1nj4zxmDkFkarn9E5Ri_Ko34WCfU6s4vQV3NaneMx--Y2Y-6$
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!FaxH778!I8kXbi2qAeGP5ieQ1nj4zxmDkFkarn9E5Ri_Ko34WCfU6s4vQV3NaneMx--Y2Y-6$
 

This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to