And this seems to be the difference between the Classification of the 
Occupancy/Commodity (hard part performed by EOR) and figuring out what 
sprinkler and spacing to use in a particular compartment with clouds, soffits, 
skylights, beams, joists, hidden spaces, piping configuration, hanger 
placement, bracing, hydraulic calcs, submittals, etc. (easy part performed by 
sprinkler designer/contractor).

Just joking about who has the easy part.

Bill Brooks (Member)

William N. Brooks P.E.
Brooks Fire Protection Engineering Inc.

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Ed Kramer via Sprinklerforum
Sent: Tuesday, October 12, 2021 4:05 PM
To: [email protected]
Cc: Ed Kramer <[email protected]>
Subject: RE: mixing EC sprinks with SC sprinks

I think making the new SC sprinklers standard-response is the best solution in 
this particular situation.

I could see these EC sprinklers being used as both 20'x20' and 14'x14' in
the same compartment in order to protect odd-ball areas.   Then adding new
SC sprinklers and deciding if they should be QR or SR gets more complicated.
I was hoping 13 would provide guidance.

Ed

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Taylor Schumacher via Sprinklerforum
Sent: Tuesday, October 12, 2021 2:31 PM
To: [email protected]
Cc: Taylor Schumacher <[email protected]>
Subject: RE: mixing EC sprinks with SC sprinks

We follow how they are listed. If the 3mm bulbs are spaced at SR, we utilize SR 
5mm bulbs for adjacent standard coverage sprinklers. 


Taylor Schumacher



-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Mike Morey via Sprinklerforum
Sent: Tuesday, October 12, 2021 2:23 PM
To: [email protected]
Cc: Mike Morey <[email protected]>
Subject: RE: mixing EC sprinks with SC sprinks

I would say if they're all being used as an SR sprinkler based on listing, I 
would put in SR sprinklers.  Is there an AHJ you can lean on?  That's what I 
would approach them with as far as logic.

Mike Morey
CFPS 3229 * NICET S.E.T. 123677
Project Manager * Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive * Fort Wayne, IN * 46825 direct 260.487.7824 /  cell
260.417.0625 /  fax 260.487.7991 email [email protected]



-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Ed Kramer via Sprinklerforum
Sent: Tuesday, October 12, 2021 3:16 PM
To: [email protected]
Cc: Ed Kramer <[email protected]>
Subject: mixing EC sprinks with SC sprinks

 
BE ADVISED - This email originated outside EMCOR. 
 

Forumities,

This has likely been previously addressed, but it's just not coming back to me 
. . .

 

I've got an existing ordinary hazard area that is protected by existing EC 
sprinklers.  The existing EC sprinklers have fast response (3mm) elements and 
are listed as standard-response for the 20'x20' spacing they are protecting.  
If these sprinklers were protecting an area of 14' x 14', they would be listed 
as quick-response.

 

I need to add a couple standard-coverage sprinklers due to wall changes.
Should the new standard-coverage sprinklers be quick-response, or 
standard-response?

 

NFPA 13 (2019) section
https://urldefense.proofpoint.com/v2/url?u=https-3A__urldefense.com_v3_-5F-5Fhttp-3A__9.4.3.5-5F-5F-3B-21-21FaxH778-21NjvBLXYl2Y98ErgMyq9iF&d=DwICAg&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=iih4NVEkD89x14qk7m6LbFsl49j-eQ0kuCE55fl2VOI&m=EQOAnHh_Yu58O-jJpDHThSpSw5Wxu_LAvMSKgI0iFfk&s=B08Eq9KCGacJUUOrNuBeq7Iqs8lYnP1nzgcOejLRTVc&e=
VRSvqAUyYKBmSwdF1FH-Y30MG_-ngt9IAYtt0y1QUQd$  gives me guidance if I were 
adding an identical EC sprinkler, but that's not what's happening.

 

Thanks in advance,

Ed K

 

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=https-3A__urldefense.com_v3_-5F-5Fhttp-3A__lists.firesprinkler.org_listinfo.cgi_spri&d=DwICAg&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=iih4NVEkD89x14qk7m6LbFsl49j-eQ0kuCE55fl2VOI&m=EQOAnHh_Yu58O-jJpDHThSpSw5Wxu_LAvMSKgI0iFfk&s=bVdSWiH7RabLavK2IkHtJ3etG4jTD1-nF7_bYmzd7Mo&e=
nklerforum-firesprinkler.org__;!!FaxH778!NjvBLXYl2Y98ErgMyq9iFVRSvqAUyYKBmSw
dF1FH-Y30MG_-ngt9IAYttwf-jBd3$ 

This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=iih4NVEkD89x14qk7m6LbFsl49j-eQ0kuCE55fl2VOI&m=EQOAnHh_Yu58O-jJpDHThSpSw5Wxu_LAvMSKgI0iFfk&s=_bOn6z1rYbf3ecSS-zAlaxmLuARh7gr1rXJSKO3m2lg&e=

_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=iih4NVEkD89x14qk7m6LbFsl49j-eQ0kuCE55fl2VOI&m=EQOAnHh_Yu58O-jJpDHThSpSw5Wxu_LAvMSKgI0iFfk&s=_bOn6z1rYbf3ecSS-zAlaxmLuARh7gr1rXJSKO3m2lg&e=

_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=iih4NVEkD89x14qk7m6LbFsl49j-eQ0kuCE55fl2VOI&m=EQOAnHh_Yu58O-jJpDHThSpSw5Wxu_LAvMSKgI0iFfk&s=_bOn6z1rYbf3ecSS-zAlaxmLuARh7gr1rXJSKO3m2lg&e=
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to