I would say if they're all being used as an SR sprinkler based on listing, I 
would put in SR sprinklers.  Is there an AHJ you can lean on?  That's what I 
would approach them with as far as logic.

Mike Morey
CFPS 3229 * NICET S.E.T. 123677
Project Manager * Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive * Fort Wayne, IN * 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]



-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Ed Kramer via Sprinklerforum
Sent: Tuesday, October 12, 2021 3:16 PM
To: [email protected]
Cc: Ed Kramer <[email protected]>
Subject: mixing EC sprinks with SC sprinks

 
BE ADVISED - This email originated outside EMCOR. 
 

Forumities,

This has likely been previously addressed, but it's just not coming back to me 
. . .

 

I've got an existing ordinary hazard area that is protected by existing EC 
sprinklers.  The existing EC sprinklers have fast response (3mm) elements and 
are listed as standard-response for the 20'x20' spacing they are protecting.  
If these sprinklers were protecting an area of 14' x 14', they would be listed 
as quick-response.

 

I need to add a couple standard-coverage sprinklers due to wall changes.
Should the new standard-coverage sprinklers be quick-response, or 
standard-response?

 

NFPA 13 (2019) section 
https://urldefense.com/v3/__http://9.4.3.5__;!!FaxH778!NjvBLXYl2Y98ErgMyq9iFVRSvqAUyYKBmSwdF1FH-Y30MG_-ngt9IAYtt0y1QUQd$
  gives me guidance if I were adding an identical EC sprinkler, but that's not 
what's happening.

 

Thanks in advance,

Ed K

 

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!FaxH778!NjvBLXYl2Y98ErgMyq9iFVRSvqAUyYKBmSwdF1FH-Y30MG_-ngt9IAYttwf-jBd3$
 

This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to