I was looking at NFPA 13 - 2019 16.3.2 "when steel pipe referenced in 7.3.1.1 
is used... ...minimum nominal wall thickness for pressures up to 300psi shall 
be in accordance with Schedule 10..."

Does this require that thinner pipe be listed?

I was curious if the listed s7/s5 products are any different from plain ASTM 
A53 pipes.

Matt 

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of John Denhardt via Sprinklerforum
Sent: Wednesday, January 20, 2021 1:30 PM
To: [email protected]
Cc: John Denhardt <[email protected]>
Subject: Re: schedule 7 pipe?

Keep in mind, NFPA 13 states piping or tubing that meets Table 7.3.1.1 is 
acceptable.  Listing is NOT required.

*NFPA 13 - 2019:  7.3.1.1 Pipe or tube shall meet or exceed one of the 
standards in Table 7.3.1.1 or be in accordance with 7.3.3.*

Thus, as long as any piping or tubing material complies with one of the 
standards listed in Table 7.3.1.1, it is acceptable to use.

I have not used much schedule 7 steel pipe in my career.  However, I have heard 
many horror stories with this steel pipe.

Thanks,
John

John August Denhardt, PE
*Vice President, Engineering and Technical Services*

*American Fire Sprinkler Association*
m: p: 301-343-1457
214-349-5965 ext 121
w: 
https://linkprotect.cudasvc.com/url?a=https%3a%2f%2ffiresprinkler.org&c=E,1,bWryeR7tZ1O1dLjO_NhXR7V9rqsGxiLcfcfxT61KfaRhT9d0vtjwLH8mf5H5b3CwfLZsk5y7lN7JEH9NkkBgwe6xh-RXiPwz27rNQL7VVbhK0GqIrDj-jw,,&typo=1
<https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/afsa/status/1039528345367732224>
<https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
   <https://www.instagram.com/firesprinklerorg/>

*Our members are at the heart of everything we do.*


*Expand your design department in 2021!* AFSA is taking its popular two-week 
Beginning Fire Sprinkler System Planning School on the road. From San Diego to 
Tampa Bay and stops in between, our technical experts will teach the basics of 
system layout based on the 2019 edition of NFPA 13. Space is limited. Enroll 
today at
https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fwww.firesprinkler.org%2fschools.&c=E,1,qs9LkaxPeR7tDIQVW9-azgrqbr53d67A6UYAwcltYiDIbtUt4GfBVOY5w9T6n83ucR00o4SIsFz_q3_gR4EGrMhmFr-YMwlwqmHdCnLepyggICEUFCpe-zlJxUU,&typo=1


On Wed, Jan 20, 2021 at 10:58 AM Matt Grise via Sprinklerforum < 
[email protected]> wrote:

> Has there been any push/interest in allowing unlisted (standard ASTM 
> A53) schedule 7 steel pipe to be allowed by code in place of the listed "flow"
> piping options?
>
> Matt
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> https://linkprotect.cudasvc.com/url?a=http%3a%2f%2flists.firesprinkler
> .org%2flistinfo.cgi%2fsprinklerforum-firesprinkler.org&c=E,1,7rii8OKXA
> UAY3sTqr74qkb_8u6tIjZP00BTkd2h-2502Sweaf0f3SP94B6veam2pdmTDTc3twqER3RP
> e1aQyyUnqyk7j-P2PXtCTbxR8HeD3w1x7AqViLzPK&typo=1
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://linkprotect.cudasvc.com/url?a=http%3a%2f%2flists.firesprinkler.org%2flistinfo.cgi%2fsprinklerforum-firesprinkler.org&c=E,1,MYY-2t_MWoEpGuIZq0hFfqzvPlgneE0QsS5c3SP_vYWPZ6OR1IsDv33M31SO90CHonz-mxqtB8VHDR5dwDD-w_5SpIWGm-s2zq52hKU0Ijw-irZH5p4l160-FmM,&typo=1
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to