Keep in mind, NFPA 13 states piping or tubing that meets Table 7.3.1.1 is
acceptable.  Listing is NOT required.

*NFPA 13 - 2019:  7.3.1.1 Pipe or tube shall meet or exceed one of the
standards in Table 7.3.1.1 or be in accordance with 7.3.3.*

Thus, as long as any piping or tubing material complies with one of the
standards listed in Table 7.3.1.1, it is acceptable to use.

I have not used much schedule 7 steel pipe in my career.  However, I have
heard many horror stories with this steel pipe.

Thanks,
John

John August Denhardt, PE
*Vice President, Engineering and Technical Services*

*American Fire Sprinkler Association*
m: p: 301-343-1457
214-349-5965 ext 121
w: firesprinkler.org
<https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/afsa/status/1039528345367732224>
<https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
   <https://www.instagram.com/firesprinklerorg/>

*Our members are at the heart of everything we do.*


*Expand your design department in 2021!*
AFSA is taking its popular two-week Beginning Fire Sprinkler System
Planning School on the road. From San Diego to Tampa Bay and stops in
between, our technical experts will teach the basics of system layout based
on the 2019 edition of NFPA 13. Space is limited. Enroll today at
https://www.firesprinkler.org/schools.


On Wed, Jan 20, 2021 at 10:58 AM Matt Grise via Sprinklerforum <
[email protected]> wrote:

> Has there been any push/interest in allowing unlisted (standard ASTM A53)
> schedule 7 steel pipe to be allowed by code in place of the listed "flow"
> piping options?
>
> Matt
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to