[RE-wrenches] Sol-Ark arc fault issues

2022-05-10 Thread Eric Smiley via RE-wrenches
A general question for those who have installed Sol-Ark. We have a handful of systems that have consistently displayed arc-faults that, as best as we can determine, are false positives. Is this something others have experienced? We are trying to determine if this is a general problem with Sol-Ark o

Re: [RE-wrenches] Magnum inverter/generator integration problems

2022-07-25 Thread Eric Smiley via RE-wrenches
Also check bonding and ground loops (e.g. genny neutral bonded and also bonded at main panel). This can cause voltage to bounce around and the inverter won't sync. *Eric Smiley,* Project Manager e...@vecoop.ca T: 250.703.6004 <+12507036004> T: 888.386.0116 <+18883860116> *VIRIDIANENERGY.CA

Re: [RE-wrenches] GT inverter for SWWP turbine

2022-08-11 Thread Eric Smiley via RE-wrenches
Skybox is discontinued and tech support is limited. There are still significant software issues with them that make them unreliable for battery back-up. We are in the process of replacing the 3 Skyboxes we wish we had never installed. *Eric Smiley,* Project Manager e...@vecoop.ca T: 250.703.6004

Re: [RE-wrenches] Battery Monitor for Li

2022-09-02 Thread Eric Smiley via RE-wrenches
I am having the same problem - same situation. I am going to tweak the efficiency value and see if it helps. *Eric Smiley,* Project Manager e...@vecoop.ca T: 250.703.6004 <+12507036004> T: 888.386.0116 <+18883860116> *VIRIDIANENERGY.CA * *

[RE-wrenches] Old Birdhouse systems

2022-09-07 Thread Eric Smiley via RE-wrenches
We have some older systems that used the MidNite Disco Combiners and Birdhouse. We have to install a new Rapid Shutdown system since these can't be replaced. My question is, can I quickly/easily disable the Rapid Shutdown in the Combiner and still use it as a combiner? What is the signal in the C

Re: [RE-wrenches] 3 phase off-grid UL listed

2022-09-08 Thread Eric Smiley via RE-wrenches
I've worked with a few larger 3-phase Conext XW systems - 3 inverters and 6 inverters. The inverters' output capabilities are slightly reduced since they have to be converted to 120 V, effectively doubling the output current. Also,they required an external transfer switch. Even with 3 inverters con

Re: [RE-wrenches] AC Coupling Standard?

2022-12-02 Thread Eric Smiley via RE-wrenches
Utilities have used and continue to use this method of control for their own generators, except they refer to it as Droop Control. In addition to Frequency/Watt response Voltage/VAR response is also used. https://en.wikipedia.org/wiki/Droop_speed_control Building inverters that mimic the behaviour

[RE-wrenches] XWPro produces noise at low (<50 W Power)

2022-12-06 Thread Eric Smiley via RE-wrenches
The inverter produces acceptable noise under no-load and at loads above 50 W or so. The noise (humming/buzzing) increases drastically at low power. So, essentially it makes a lot of noise at night. Has anyone else encountered this? We suspect it is the transformer vibrating - some kind of resonance

Re: [RE-wrenches] XWPro produces noise at low (<50 W Power)

2022-12-06 Thread Eric Smiley via RE-wrenches
LL factory defaults and reenter your grid code. > If you find this a bit confusing, Tech support IS QUITE supportive. > > On Dec 5, 2022, at 11:52 AM, Eric Smiley via RE-wrenches < > re-wrenches@lists.re-wrenches.org> wrote: > > The inverter produces acceptable noise under

Re: [RE-wrenches] Lithium battery recommendation

2023-07-13 Thread Eric Smiley via RE-wrenches
Keep in mind the Fortress eVault is a 500 lb beast. Our installers complained about it and we've moved to smaller, rack-mount units and are currently testing the HomeGrid Stack'd in various configurations. *Eric Smiley,* Design Manager e...@vecoop.ca T: 250.703.6004 <+12507036004> T: 888.386.0116

Re: [RE-wrenches] Schneider XW+ Repair

2023-08-01 Thread Eric Smiley via RE-wrenches
Last time I had an AC relay go, I ordered a board from Mark Snyder. mseproje...@marksnyderelectric.com Eric Smiley Design Manager E: e...@vecoop.ca T: 1-888-386-0116 ext 702 (toll free) C: 250-703-6004 W: viridianenergy.ca On Tue., Aug. 1, 2023, 16:00 Andrew Perkins via RE-wrenches, < re-w

Re: [RE-wrenches] Fronius USA available 2023 & 2024 ?

2023-08-25 Thread Eric Smiley via RE-wrenches
Interesting. Fronius has a strong presence in Canada with good tech support. We also have a very low failure rate - can't remember the last time we replaced one. There were some supply issues earlier this year but we are receiving inverters and parts. They also have a good rep for low failure and g

Re: [RE-wrenches] Off Grid, Cloudy Days, Solar Tilt Question

2023-10-25 Thread Eric Smiley via RE-wrenches
It is difficult to quantify but this was pointed out to me years ago by a long-time off-grid installer, who also lives off grid on Vancouver Island where weeks of solid cloud isn't unusual. We never tilt to latitude + 10 to 15 for off-grid, as many textbooks recommend. Latitude works quite well. Wh

Re: [RE-wrenches] Grid Tied Inverter back feed to Generator

2023-12-01 Thread Eric Smiley via RE-wrenches
We were called to repair a system where this happened. All the micro inverters were fried and so was the generator. It caused a voltage rise that the monitoring system recorded at 348 V before it went down, when the PV ran the generator as a motor. *Eric Smiley,* Design Manager e...@vecoop.ca T:

Re: [RE-wrenches] Fortress

2024-02-14 Thread Eric Smiley via RE-wrenches
The BMS in the eVault Classic has been a headache. Fortunately, we were able to convince Fortress to let us proactively replace the BMS in some of our systems - especially the remote off-grid systems. We are still having problems with weird SOC readings on many of the batteries. Apparently the SOC

[RE-wrenches] Huawei inverter tech support

2024-02-14 Thread Eric Smiley via RE-wrenches
We have a client with a Huawei 9KTL-USL0 who recently contacted us about his system. Does anyone know how to obtain tech support in NA for these products? *Eric Smiley,* Design Manager e...@vecoop.ca T: 250.703.6004 <+12507036004> T: 888.386.0116 <+18883860116> *VIRIDIANENERGY.CA

Re: [RE-wrenches] Sol-Ark 15k solar panel frame grounding

2024-06-05 Thread Eric Smiley via RE-wrenches
SolArk arrays are ungrounded. However, because they are transformerless, when the inverter is operating, there is a reference to ground on the DC side via the AC side neutral bond to ground. So, a ground fault on the AC side will also cause a GF error. Many transformerless interactive inverters ar

Re: [RE-wrenches] AES RACK MOUNT

2024-07-17 Thread Eric Smiley via RE-wrenches
If you want UL9540, the AES rackmount has to be in the Slimline enclosure. Eric Smiley (he/him) - Design Manager 250.703.6004 e...@vecoop.ca 888.386.0116 3-4997 Polkey Rd, Duncan BC, V9L 6W3 viridiansolar.ca

Re: [RE-wrenches] All-In-Ones / Sol-Ark fail

2024-10-10 Thread Eric Smiley via RE-wrenches
Install stand-alone charge controllers. That is the only way to get redundancy. Eric Smiley (he/him) - Design Manager 250.703.6004 e...@vecoop.ca 888.386.0116 3-4997 Polkey Rd, Duncan BC, V9L 6W3 viridiansolar.ca

Re: [RE-wrenches] Lead acid batteries taking too much current

2024-10-04 Thread Eric Smiley via RE-wrenches
Our company does not pair any lead acid with a Sol-Ark. Our opinion is that the unit is designed for Li-Ion and that is what should be used. In much the same way that some legacy off-grid products don't play nicely with Li-Ion, we stick with combinations that don't require specialized programming w

Re: [RE-wrenches] AGM battery recommendations

2025-01-13 Thread Eric Smiley via RE-wrenches
The disparity in cycle life can sometimes be due to different test standards for cycle life evaluation. I'm familiar with three standards that are commonly used by manufacturers: 1. IEC 61427 2. IEC 60896-2 3. BCIS-06 The IEC 61427 standard is specifically for Solar PV applications. Eri