Has anyone dealt with a large ESS installation that exceeds the aggregate
storage limits in NFPA 855? The limits are quite low for very large single
family homes. I have a situation where we need 120 kWh minimum for an
off-grid home. There is a building dedicated for the inverters and
batteries tha
I'm not looking at the most recent editions right, but the previous
versions of both 855 and the IRC both have statements to the effect of "ESS
installations exceeding the permitted individual or aggregate ratings shall
be installed in accordance with Section xxx" (pointing to the IFC in the
case o
That is how I am reading it. Complying with chapters 4 through 9 would be
required. However, I think it will be impossible to comply given the fire
suppression requirements. This is a remote off-grid installation, and water
supply would be an issue. And I'm not sure how to go about finding someone
Hi Jason, these might help:
When agreeable with the ESS owner and approved by the AHJ, fire suppression
systems and water supply are permitted to be omitted:
●IFC 1207.8 Where approved by the AHJ, the fire control and suppression
systems, the size and separation requirements, and the water supply
I would add to this that the size of the lag is a factor too. 3/8" lags
into 1-1/2" wide rafters are going to cause much more damage, and leave
larger voids, than the new 1/4" high strength lags I use now. I like
the rafter sistering idea, as a solution, as well as moving the rails up
or down
Scott,
For liability you might want a before and after inspection by a really
top inspector that you trust.
I would also ask your insurance for guidance. My insurance is always
telling me that going out of business is the typical last
straw for roofers.
Build a solar pergola😉
Dave Angelini
Great, thoughtful answers from all. I’m going to push this to the
FineHomeBuilding podcast crew for their ideas, too.
I hate to ask the question I might not want to hear the answer to, but I can’t
think of anything more horrible than a failed rafter. That would be the resi
equivalent of the inf
Of the other 2 or 3. PIKAs you installed are you aware of any failures? I
installed one at my place and had to sell it to one of'
my customers when I found out that they were sold out, not aware that
they were not going to make any more.
It worked great for me and is still running fine at my custo
Jeremy,
You looking for new or used?
Bill
Feather River Solar Electric
Bill Battagin, owner
4291 Nelson St. (Shipping)
5575 Genesee Rd. (USPS, UPS)
Taylorsville, CA 95983
530-284-7849, 258-1641(cell)
CA. C10 Lic # 874049
Solar Powered since 1982
Home of the Sunny Side Up
On 5/28/2
Jeremy,
You looking for new or used? Could it be a -40?
Bill
Feather River Solar Electric
Bill Battagin, owner
4291 Nelson St. (Shipping)
5575 Genesee Rd. (USPS, UPS)
Taylorsville, CA 95983
530-284-7849, 258-1641(cell)
CA. C10 Lic # 874049
Solar Powered since 1982
Home of the Sunn
Jason,
I called SimpliPhi on this before I added 4 more 3.8M
(white, steel case) to a pack of 8 of the older black plastic case
3.8's. They told me it was no problem, this now pack of 12 has been in
service for about 7 months. Of course there is a procedure for marrying
batterie
To be clear, I asked SimpliPhi only about their open comm 48V 3.8 batteries.
Bill
Feather River Solar Electric
Bill Battagin, owner
4291 Nelson St. (Shipping)
5575 Genesee Rd. (USPS, UPS)
Taylorsville, CA 95983
530-284-7849, 258-1641(cell)
CA. C10 Lic # 874049
Solar Powered since 1982
Home of t
The change from Black case to White case was about 3.5 years ago. The
current white case version is either open loop (SimpliPhi 3.8M) or
closed loop (AmpliPhi 3.8M)